NEMA 3 Exterior Meter/Main Combo.Is the enclosure NEMA rated to be exposed to water?
No idea. Photos sent to me by the owner.Is the fence within the NEC required working clearances?
Yesis that patchy area to the left indicative of a CMU wall
Aren't all windows? I'll find out if it's a bathroom. Really, really small window..Is the window required for ventilation?
They don't even know that this is down here. No frost and nothing but sand.300.5 Earth Movement. Conduit needs a slip-joint
The Earth still moves...It revolves around the NEC doesn't it?They don't even know that this is down here. No frost and nothing but sand.
The lack of discoloration on the wall leads me away from that draining water.It appears there is an overflow drain or condensate drain above it.
It is the conduit that they will connect to to take the feeders into the MLS panels inside.The lack of discoloration on the wall leads me away from that draining water.
110.12 Mechanical execution of work
110.13 (A) Mounting
300.5 Earth Movement. Conduit needs a slip-joint
No, not all windows are required by code for ventilation.Is the window required for ventilation?
Aren't all windows? I'll find out if it's a bathroom. Really, really small window.
The wire from FPL is too short for them to move it so they will have to get them to change out the lateral or find some slack from the POCO transformer.Does the meter socket have the feeder entrance hole where the conduit is located, does the feeder have to enter on the left or could the installer placed the hole more to the right?
Is is absolutely enforceable which is why it exists.110.12: "Electrical equipment shall be installed in a neat and workmanlike manner." This language is vague and hence unenforceable.
110.12 violates the NEC Style Guide, which says in 3.2.1 "The documents shall not contain references or requirements that are unenforceable or vague. The terms contained in Table 3.2.1 shall be reviewed in context, and if the resulting requirement is unenforceable or vague, the term shall not be used." Table 3.2.1 includes both the terms "Neat" and "Workmanlike".Is is absolutely enforceable which is why it exists.
What code section was cited?So for the record, this was rejected just to let you know.
Is is absolutely enforceable which is why it exists.
None. The owner asked me to look at it in person, and when I got there, he told me they had decided to properly install it and were replacing it.What code section was cited?
Is that how drafting guides work in the US?110.12 violates the NEC Style Guide, which says in 3.2.1 "The documents shall not contain references or requirements that are unenforceable or vague. The terms contained in Table 3.2.1 shall be reviewed in context, and if the resulting requirement is unenforceable or vague, the term shall not be used." Table 3.2.1 includes both the terms "Neat" and "Workmanlike".
110.12 is vague and unenforceable. It's like a requirement that says "electrical installations shall not be ugly." There is no objective standard to apply.
Now, if 110.13(A) on Mounting included a requirement like "Any enclosure with a face larger than 12" x 12" installed against a wall shall be supported within 3" of each corner of that face," that's an objective standard and we can say that the picture in the OP violates it. But 110.13(A) does not say that, and the picture in the OP is not an NEC violation.
Cheers, Wayne
110.12 violates the NEC Style Guide, which says in 3.2.1 "The documents shall not contain references or requirements that are unenforceable or vague. The terms contained in Table 3.2.1 shall be reviewed in context, and if the resulting requirement is unenforceable or vague, the term shall not be used." Table 3.2.1 includes both the terms "Neat" and "Workmanlike".
110.12 is vague and unenforceable. It's like a requirement that says "electrical installations shall not be ugly." There is no objective standard to apply.
Now, if 110.13(A) on Mounting included a requirement like "Any enclosure with a face larger than 12" x 12" installed against a wall shall be supported within 3" of each corner of that face," that's an objective standard and we can say that the picture in the OP violates it. But 110.13(A) does not say that, and the picture in the OP is not an NEC violation.
Cheers, Wayne
And that is precisely what you don't seem to understand about this industry. Not everything is specific, but those in the industry understand why not everything can be or should be specific.There is no objective standard to apply.