When Are Ground Rods Required at a Generator?

jar546

CBO
Joined
Oct 16, 2009
Messages
12,805
Location
Not where I really want to be
I've only seen a handful of installations that required this. As a matter of fact, I can probably count them on one hand. There are situations where ground rods are required at a generator. Who knows the answer as to under what circumstances ground rods are required at a generator?

ChatGPT Image May 15, 2025, 07_52_43 AM.png
 
When it is a separately derived system
Does not require ground rods at the generator, merely requires a GEC (Grounding Electrode Conductor) to a GES (Grounding Electrode System). The adjacent building's GES could be used. In fact if the generator is sufficiently close to the structure, any ground rods you install for it must be connected back to the building's GES.

The only requirement I can see for a ground rod at the generator itself would be 110.3(B), if the listing standard requires one. Of course, until the 2020 NEC generators weren't required to be listed.

Cheers, Wayne
 
Does not require ground rods at the generator, merely requires a GEC (Grounding Electrode Conductor) to a GES (Grounding Electrode System). The adjacent building's GES could be used. In fact if the generator is sufficiently close to the structure, any ground rods you install for it must be connected back to the building's GES.

The only requirement I can see for a ground rod at the generator itself would be 110.3(B), if the listing standard requires one. Of course, until the 2020 NEC generators weren't required to be listed.

Cheers, Wayne
And what is that sufficiently close dimension in the NEC again?....Yes, they could use some other grounding electrode, such as rebar in the concrete supports, but my point was that it did not need it's own GES unless it was an SDS....But even that answer could be a little fluid...
 