That is not the answer we are looking for. We are looking for an NEC-driven answer that not only changes the ground rod requirements, but how the system is wired and disconnected.When the plans require them.
Does not require ground rods at the generator, merely requires a GEC (Grounding Electrode Conductor) to a GES (Grounding Electrode System). The adjacent building's GES could be used. In fact if the generator is sufficiently close to the structure, any ground rods you install for it must be connected back to the building's GES.When it is a separately derived system
And what is that sufficiently close dimension in the NEC again?....Yes, they could use some other grounding electrode, such as rebar in the concrete supports, but my point was that it did not need it's own GES unless it was an SDS....But even that answer could be a little fluid...Does not require ground rods at the generator, merely requires a GEC (Grounding Electrode Conductor) to a GES (Grounding Electrode System). The adjacent building's GES could be used. In fact if the generator is sufficiently close to the structure, any ground rods you install for it must be connected back to the building's GES.
The only requirement I can see for a ground rod at the generator itself would be 110.3(B), if the listing standard requires one. Of course, until the 2020 NEC generators weren't required to be listed.
Cheers, Wayne
I started this thread to educate, not debate technicalities. Far too often, I’ve seen inspectors call for ground rods at generators without understanding why. Many don’t know what a separately derived system actually is, let alone when it applies. Most residential inspectors may go their whole career without seeing one. And yet, they’re out there calling for ground rods by default, even when the generator doesn't require it. Meanwhile, they’re missing the bigger issue, like a neutral-to-ground bond in a non-SDS installation, which I’ve personally found on follow-up inspections.Does not require ground rods at the generator, merely requires a GEC (Grounding Electrode Conductor) to a GES (Grounding Electrode System). The adjacent building's GES could be used. In fact if the generator is sufficiently close to the structure, any ground rods you install for it must be connected back to the building's GES.
The only requirement I can see for a ground rod at the generator itself would be 110.3(B), if the listing standard requires one. Of course, until the 2020 NEC generators weren't required to be listed.
Cheers, Wayne