2018 IBC 1009.2.1 and "accessible" floors - R-2
admiralArchArch
middle earth
I have two 5 story R-2 (VA) buildings with on level S-2 enclosed parking garage (4 total R-2 stories, NFPA13R). We have an elevator serving all floors. There are no what would be considered "common use areas", only stairs, corridors and the elevator (exception of the mail room on level 1). I had assumed the whole time that per 1009.2.1 that I need to provide an generator in order to have a required elevator serving as a accessible means of egress complying with 1009.4. However, I am starting to doubt that we need standby power because of the portion that says "where a required accessible floor..."
Note that my jurisdiction deletes chapter 11 of the IBC and defers to state accessibility guidelines (ADA 2010).
We have about 36 units per building, per ADA I only need two units with communication features, and one with mobility features. I have located these on the level just above the parking garage, level 2. If I have no accessible units (ie Type A) on the fifth floor, than does that mean that I do not have a required accessible floor?
203.8 Residential Facilities. In residential facilities, common use areas that do not serve residential dwelling units required to provide mobility features complying with 809.2 through 809.4 shall not be required to comply with these requirements or to be on an accessible route.
233.3.1.1 Residential Dwelling Units with Mobility Features. In facilities with residential dwelling units, at least 5 percent, but no fewer than one unit, of the total number of residential dwelling units shall provide mobility features complying with 809.2 through 809.4 and shall be on an accessible route as required by 206.
206.2.3 Multi-Story Buildings and Facilities. At least one accessible route shall connect each story and mezzanine in multi-story buildings and facilities.
EXCEPTIONS:
  1. In private buildings or facilities that are less than three stories or that have less than 3000 square feet (279 m2) per story, an accessible route shall not be required to connect stories provided that the building or facility is not a shopping center, a shopping mall, the professional office of a health care provider, a terminal, depot or other station used for specified public transportation, an airport passenger terminal, or another type of facility as determined by the Attorney General.
  2. Where a two story public building or facility has one story with an occupant load of five or fewer persons that does not contain public use space, that story shall not be required to be connected to the story above or below.
  3. In detention and correctional facilities, an accessible route shall not be required to connect stories where cells with mobility features required to comply with 807.2, all common use areas serving cells with mobility features required to comply with 807.2, and all public use areas are on an accessible route.
  4. In residential facilities, an accessible route shall not be required to connect stories where residential dwelling units with mobility features required to comply with 809.2 through 809.4, all common use areas serving residential dwelling units with mobility features required to comply with 809.2 through 809.4, and public use areas serving residential dwelling units are on an accessible route.
  5. Within multi-story transient lodging guest rooms with mobility features required to comply with 806.2, an accessible route shall not be required to connect stories provided that spaces complying with 806.2 are on an accessible route and sleeping accommodations for two persons minimum are provided on a story served by an accessible route.
  6. In air traffic control towers, an accessible route shall not be required to serve the cab and the floor immediately below the cab.
  7. Where exceptions for alterations to qualified historic buildings or facilities are permitted by 202.5, an accessible route shall not be required to stories located above or below the accessible story.
ADASAD does not apply to multifamily housing. The Fair Housing Act Amendments apply to new construction of housing built for first occupancy after March 13, 1991. This is where Type A & B units come from.
Even though your state deleted IBC Chapter 11 your client could still be sued under the Fair Housing Act for not complying with these amendments.
Unless it's public housing. Then the 2010 ADAS applies.
But yeah, if there's types A and B required, that's not ADAS.
In that case, I'd say you're correct that an accessible route does not need to connect the non-accessible floors (anything above level 2).
Thank you. I am starting to learn that ADA isn't considered "safe harbor" by FHA. These units without mobility features would then be considered "covered" units by the FHA. Does that make them on an "accessible floor"?. BTW Accessible Story is italicized in the IBC but there is no definition for go figure.
Here's a screenshot form the FHA design manual:
FHA isn't my specialty. My experience is with ADAS, so grain of salt with what I'm about to write since there might be an exception I don't know about somewhere.
My understanding is that "covered multifamily dwellings" consist of the following (incomplete list):
1. All dwelling units (regardless of story) in buildings with more than 4 units with an elevator.
2. All ground-floor dwelling units in buildings with 4 or more units but NO elevator.
If the elevator doesn't meet that exception above (screenshot), then I believe all units in the building are covered.