admiralArchArch
I have two 5 story R-2 (VA) buildings with on level S-2 enclosed parking garage (4 total R-2 stories, NFPA13R). We have an elevator serving all floors.  There are no what would be considered "common use areas", only stairs, corridors and the elevator (exception of the mail room on level 1).  I had assumed the whole time that per 1009.2.1 that I need to provide an generator in order to have a required elevator serving as a accessible means of egress complying with 1009.4.  However, I am starting to doubt that we need standby power because of the portion that says "where a required accessible floor..."
Note that my jurisdiction deletes chapter 11 of the IBC and defers to state accessibility guidelines (ADA 2010).
We have about 36 units per building, per ADA I only need two units with communication features, and one with mobility features. I have located these on the level just above the parking garage, level 2. If I have no accessible units (ie Type A) on the fifth floor, than does that mean that I do not have a required accessible floor?
203.8 Residential Facilities. In residential facilities, common use areas that do not serve residential dwelling units required to provide mobility features complying with 809.2 through 809.4 shall not be required to comply with these requirements or to be on an accessible route.
233.3.1.1 Residential Dwelling Units with Mobility Features. In facilities with residential dwelling units, at least 5 percent, but no fewer than one unit, of the total number of residential dwelling units shall provide mobility features complying with 809.2 through 809.4 and shall be on an accessible route as required by 206.
206.2.3 Multi-Story Buildings and Facilities. At least one accessible route shall connect each story and mezzanine in multi-story buildings and facilities.
EXCEPTIONS:
- In private buildings or facilities that are less than three stories or that have less than 3000 square feet (279 m2) per story, an accessible route shall not be required to connect stories provided that the building or facility is not a shopping center, a shopping mall, the professional office of a health care provider, a terminal, depot or other station used for specified public transportation, an airport passenger terminal, or another type of facility as determined by the Attorney General.
- Where a two story public building or facility has one story with an occupant load of five or fewer persons that does not contain public use space, that story shall not be required to be connected to the story above or below.
- In detention and correctional facilities, an accessible route shall not be required to connect stories where cells with mobility features required to comply with 807.2, all common use areas serving cells with mobility features required to comply with 807.2, and all public use areas are on an accessible route.
- In residential facilities, an accessible route shall not be required to connect stories where residential dwelling units with mobility features required to comply with 809.2 through 809.4, all common use areas serving residential dwelling units with mobility features required to comply with 809.2 through 809.4, and public use areas serving residential dwelling units are on an accessible route.
- Within multi-story transient lodging guest rooms with mobility features required to comply with 806.2, an accessible route shall not be required to connect stories provided that spaces complying with 806.2 are on an accessible route and sleeping accommodations for two persons minimum are provided on a story served by an accessible route.
- In air traffic control towers, an accessible route shall not be required to serve the cab and the floor immediately below the cab.
- Where exceptions for alterations to qualified historic buildings or facilities are permitted by 202.5, an accessible route shall not be required to stories located above or below the accessible story.