Location, Damp. Locations protected from weather and not subject to saturation with water or other liquids but subject to moderate degrees of moisture. Examples of such locations include partially protected locations under canopies, marquees, roofed open porches, and like locations, and interior locations subject to moderate degrees of moisture, such as some basements, some barns, and some cold-storage warehouses.
Location, Dry. A location not normally subject to dampness or wetness. A location classified as dry may be temporarily subject to dampness or wetness, as in the case of a building under construction.
Location, Wet. Installations under ground or in concrete slabs or masonry in direct contact with the earth; in locations subject to saturation with water or other liquids, such as vehicle washing areas; and in unprotected locations exposed to weather.
If it were me I would consider it an area that can be saturated with water or other liquid and I would require GFCI protection as per 210.8(B).In a commercial building, with concrete or tile floors (floors that will be mopped) is the floor considered a damp location needing GFCI protection?
Kinda dumb that they do food courts, but not bars or nightclubs or restaurants…Shirley they will pick that up soon and save all of us…Guess I will call it a dining area and not a food court…If it were me I would consider it an area that can be saturated with water or other liquid and I would require GFCI protection as per 210.8(B).
Also, I don’t know what edition you’re working with but in case it helps:
The 2020 made a change to 210.8(B)(6) - it is now “Indoor damp and wet locations” instead of just wet.
I also saw that the 2023 has a new section 406.4(G) - see photos.
No.In a commercial building, with concrete or tile floors (floors that will be mopped) is the floor considered a damp location needing GFCI protection?
That is true for slab-on-grade construction. I do not think that the receptacle needs to be GFCI even in this case because the box and conduit could be completely full of water without the GFCI tripping doing any good. You still would have energized screws and wiring in the water, even with the GFCI tripped, until it reached a point where it could trip an OCPD.A raceway in this scenario is a wet location. One could assume that the box is also a wet location.
I would agreeThat is true for slab-on-grade construction. I do not think that the receptacle needs to be GFCI even in this case because the box and conduit could be completely full of water without the GFCI tripping doing any good. You still would have energized screws and wiring in the water, even with the GFCI tripped, until it reached a point where it could trip an OCPD.
This logic, to me, indicates that only the parts of the fully installed receptacle that are "readily accessible" to users, need to be in a wet or damp location to require GFCI. If the box and conduit are a wet location, but the readily accessible parts are in a dry location, I would say that no GFCI protection is needed for that receptacle.