steveray
SAWHORSE
And I am absolutely good with that....But when the first stud is the jack stud holding up X000 pounds.....Or there is no jack stud and there is a metal hanger carrying the header....And they pad out the header with plywood to match the 3.5" wall....With gaps in it....Something needs to keep the fire away from the structure.Another way to think about it:
- A one hour wood-framed structural wall has to keep the structure from collapsing for one-hour (Table 602).
- A one hour separation wall (such as for occupancy separation, separating corridors from dwelling units, etc.) needs to both remain standing, and prevent burn-through for one hour. Another way to think about it is that it gets about 30 minutes to get to the center of the wall.
- OK, IBC table 723.6.2 says that in a typical wood wall where studs are 16" O/C, the studs themselves are good for 20 minutes of fire protection.
- Now imagine 2 studs butted against each other
That is why I said there are alternatives to protect the framing....What I will not say is that you do not have to protect the "exposed" structural framing in the building in VA construction...