If I am creating two separate fire areas and the Inspector said he is going to review the Residential side per the 2015 Michigan Residential code it would be reviewed as a single Family Dwelling which does not need sprinklers.Not correct if you create two separate fire areas in this case an "M" and a "R" fire areas only the "R" fire area is required to be sprinkled
2018 IEBC
1101.1 Scope.
An addition to a building or structure shall comply with the International Codes as adopted for new construction without requiring the existing building or structure to comply with any requirements of those codes or of these provisions, except as required by this chapter. Where an addition impacts the existing building or structure, that portion shall comply with this code.
1102.3 Fire protection systems.
Existing fire areas increased by the addition shall comply with Chapter 9 of the International Building Code.
If you construct a 2-hour fire barrier you are not increasing the existing fire area therefore you are not required to sprinkle the existing fire area.
Unless you can find charging language in the IEBC telling you you must comply with Chapter 9 of the IBC then 903.2.8 is not applicable
[F] 903.2 Where required.
Approved automatic sprinkler systems in new buildings and structures shall be provided in the locations described in Sections 903.2.1 through 903.2.12.