Does a R3 seprated from a use B with a 2 hr fire wall need a NFPA 13 R or 13D sprinklers? The B side does not need sprinklers.
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
Where in the code does a 2-hour fire barrier automatically make it a seperate building?High Desert said:If the two occupancies are separated by a firewall they are two separate buildings and two separate fire areas. I think it's a 13D, but I may be wrong. The B wouldn't need to be sprinklered if two separate buildings.
Two dwellings can also be a 13D.mark handler said:NFPA 13D is the standard for the “Installation of Sprinkler Systems in One and Two-Family Dwellingsand Manufactured Homes” (basically an individual unit system)
NFPA 13R is the standard for the “Installation of Sprinkler Systems in Residential Occupancies up to and
Including Four Stories in Height” (a whole building system)
Just a single R, NFPA 13D
ReRead the quoted text in your post "NFPA 13D is the standard for the “Installation of Sprinkler Systems in One and Two-Family Dwellings"brudgers said:Two dwellings can also be a 13D.
A 13D can be installed in an entire building.mark handler said:ReRead the quoted text in your post "NFPA 13D is the standard for the “Installation of Sprinkler Systems in One and Two-Family Dwellings"
13R provides references to NFPA 13 for areas that are beyond it's scope, while 13D does not contain any such reference, other than to say that 13 or 13R should be used for the residential portions of all other buildings. So I would say that 13R is much more applicable to mixed occupancy buildings. 13R covers residential buildings, so you could have a single apartment attached to the end of a shopping mall, and as long as all the appropriate code provisions are met, the building could be protected in accordance with NFPA 13R.brudgers said:13R and 13D are both designed to protect residents neither is intended to protect any other occupancy and neither is more applicable to a B or M occupancy than the other.
Is It "one" Mixed use Building?RBK said:13R provides references to NFPA 13 for areas that are beyond it's scope, while 13D does not contain any such reference, other than to say that 13 or 13R should be used for the residential portions of all other buildings. So I would say that 13R is much more applicable to mixed occupancy buildings. 13R covers residential buildings, so you could have a single apartment attached to the end of a shopping mall, and as long as all the appropriate code provisions are met, the building could be protected in accordance with NFPA 13R.
Neither 13D or 13R is applicable to anything other than residential occupancies.RBK said:13R provides references to NFPA 13 for areas that are beyond it's scope, while 13D does not contain any such reference, other than to say that 13 or 13R should be used for the residential portions of all other buildings. So I would say that 13R is much more applicable to mixed occupancy buildings. 13R covers residential buildings, so you could have a single apartment attached to the end of a shopping mall, and as long as all the appropriate code provisions are met, the building could be protected in accordance with NFPA 13R.