If you didn’t see my newbie post, this is my first time posting a question here. Go easy on me.
I am a Building Code Analyst (aka plan reviewer) in Indianapolis, IN. We currently enforce the 2006 IBC as amended by the State of IN.
I have a 7000sf non-separated, non-sprinklered mixed occupancy F-1/A-2 (brewhouse/pub - not sure why they are using F-1 classification rather than F-2, but we’ll go with it). About 3500sf for each occupancy area. They submitted a 3410 evaluation for change of occupancy in an existing building. (No IN amendments to any of the sections in question.)
Section 3410.6 states, “In applying this section to a building with mixed occupancies, where the separation between the mixed occupancies does not qualify for any category indicated in Section 3410.6.16, the score for each occupancy shall be determined and the lower score determined for each section of the evaluation process shall apply to the entire building.”
I have always interpreted that the way this evaluation works for the various sections is you use the requirements of the building to determine the category in each section, then look at each occupancy value under that category to determine the score value for that section. Then the lower of the two score values is used in Table 3410.7.
My issue is with the score they used for Section 3410.6.17 Automatic Sprinklers. I determined that the building is required to be sprinklered throughout because it is non-separated, therefore they have an A-2 “fire area” over 5000sf. (Section 3410.6.17 states “...."Required sprinklers" shall be based on the requirements of this code.” I took this to mean that Section 508.3.1.1 requirement applies to the non-separated mixed occupancy. Section 508.3.1.1 states, “...the most restrictive applicable provisions of Section 403and Chapter 9 shall apply to the entire building or portion thereof.” Section 903.2.1.2 requires sprinklers where the A-2 “fire area” exceeds 5000sf.)
So, after determining that the entire building is required to be sprinklered, I chose category a for Section 3410.6.17.1, then looking at Table 3410.6.17, I chose value of -6 for F occupancy being the most restrictive in this section.
They, on the other hand, have interpreted that when doing the evaluation, you should look at the entire building as an A-2 and then the entire building as an F to determine sprinkler requirements. So, they are saying, if you look at the entire building as an F occupancy, then it wouldn’t require sprinklers and used category c for a value of 0. They then used the A-2 value of -4 as most restrictive for the section.
My concern is that the difference between choosing -6 vs -4 for this section is the difference between pass/fail of the overall evaluation. They’ve already tweaked other sections as much as possible and have an exact passing score for fire safety.
I’ve never had a brewhouse/pub that didn’t either provide fire separation between or sprinklers throughout. Looking forward to all your input!

I have a 7000sf non-separated, non-sprinklered mixed occupancy F-1/A-2 (brewhouse/pub - not sure why they are using F-1 classification rather than F-2, but we’ll go with it). About 3500sf for each occupancy area. They submitted a 3410 evaluation for change of occupancy in an existing building. (No IN amendments to any of the sections in question.)
Section 3410.6 states, “In applying this section to a building with mixed occupancies, where the separation between the mixed occupancies does not qualify for any category indicated in Section 3410.6.16, the score for each occupancy shall be determined and the lower score determined for each section of the evaluation process shall apply to the entire building.”
I have always interpreted that the way this evaluation works for the various sections is you use the requirements of the building to determine the category in each section, then look at each occupancy value under that category to determine the score value for that section. Then the lower of the two score values is used in Table 3410.7.
My issue is with the score they used for Section 3410.6.17 Automatic Sprinklers. I determined that the building is required to be sprinklered throughout because it is non-separated, therefore they have an A-2 “fire area” over 5000sf. (Section 3410.6.17 states “...."Required sprinklers" shall be based on the requirements of this code.” I took this to mean that Section 508.3.1.1 requirement applies to the non-separated mixed occupancy. Section 508.3.1.1 states, “...the most restrictive applicable provisions of Section 403and Chapter 9 shall apply to the entire building or portion thereof.” Section 903.2.1.2 requires sprinklers where the A-2 “fire area” exceeds 5000sf.)
So, after determining that the entire building is required to be sprinklered, I chose category a for Section 3410.6.17.1, then looking at Table 3410.6.17, I chose value of -6 for F occupancy being the most restrictive in this section.
They, on the other hand, have interpreted that when doing the evaluation, you should look at the entire building as an A-2 and then the entire building as an F to determine sprinkler requirements. So, they are saying, if you look at the entire building as an F occupancy, then it wouldn’t require sprinklers and used category c for a value of 0. They then used the A-2 value of -4 as most restrictive for the section.
My concern is that the difference between choosing -6 vs -4 for this section is the difference between pass/fail of the overall evaluation. They’ve already tweaked other sections as much as possible and have an exact passing score for fire safety.
I’ve never had a brewhouse/pub that didn’t either provide fire separation between or sprinklers throughout. Looking forward to all your input!