From the link that **steveray** provided [ from the `09 IBC - Commentary ]:
`09 IBC - Commentary, TABLE 3412.6.16 - MIXED OCCUPANCY VALUESa:
[TABLE=class: MsoNormalTable]
[TR]
[TD]OCCUPANCY[/TD]
[TD=colspan: 3]CATEGORIES[/TD]
[/TR]
[TR]
[TD]a[/TD]
[TD]b[/TD]
[TD]c[/TD]
[/TR]
[TR]
[TD=width: 167] A-1, A-2, R[/TD]
[TD=width: 60]-10[/TD]
[TD=width: 60]0[/TD]
[TD=width: 60]10[/TD]
[/TR]
[TR]
[TD=width: 167] A-3, A-4, B, E, F, M, S[/TD]
[TD=width: 60]-5[/TD]
[TD=width: 60]0[/TD]
[TD=width: 60]5[/TD]
[/TR]
[/TABLE]
[TABLE=class: MsoTableGrid]
[TR]
[TD]a. For fire-resistance ratings between categories, the value shall be obtained by linear interpolation.
[/TD]
[/TR]
[/TABLE]
[TD=bgcolor: #E9E9E9] This table addresses the relative risk of a building in or close to compliance with the provisions for separated mixed occupancies.............When mixed occupancies are not separated from each other, the risk from hazards is greater in high-density occupancies, such as Groups A-1 and A-2........This risk is also greater in residential occupancies, because occupants may be sleeping and not fully alert. For this reason, inadequate separation is given greater negative values. ........In buildings with lower occupant loads, and where the occupants are alert, the risks are relatively lower. [/TD]
= = | = = | = =
From the link that **steveray** provided [ from the `09 IBC - Commentary ]:
`09 IBC - Commentary, TABLE 3412.6.16 - MIXED OCCUPANCY VALUESa:
[TABLE=class: MsoNormalTable]
[TR]
[TD]OCCUPANCY[/TD]
[TD=colspan: 3]CATEGORIES[/TD]
[/TR]
[TR]
[TD]a[/TD]
[TD]b[/TD]
[TD]c[/TD]
[/TR]
[TR]
[TD=width: 167] A-1, A-2, R[/TD]
[TD=width: 60]-10[/TD]
[TD=width: 60]0[/TD]
[TD=width: 60]10[/TD]
[/TR]
[TR]
[TD=width: 167] A-3, A-4, B, E, F, M, S[/TD]
[TD=width: 60]-5[/TD]
[TD=width: 60]0[/TD]
[TD=width: 60]5[/TD]
[/TR]
[/TABLE]
[TABLE=class: MsoTableGrid]
[TR]
[TD]a. For fire-resistance ratings between categories, the value shall be obtained by linear interpolation.
[/TD]
[/TR]
[/TABLE]
[TD=bgcolor: #E9E9E9] This table addresses the relative risk of a building in or close to compliance with the provisions for separated mixed occupancies.............When mixed occupancies are not separated from each other, the risk from hazards is greater in high-density occupancies, such as Groups A-1 and A-2........This risk is also greater in residential occupancies, because occupants may be sleeping and not fully alert. For this reason, inadequate separation is given greater negative values. ........In buildings with lower occupant loads, and where the occupants are alert, the risks are relatively lower. [/TD]
= = | = = | = =
Last edited by a moderator: