globe trekker, you mentioned in a certain circumstance exception #3 could be applied. then do you consider a tiki torch is a"gas light"?
they are a LPG mixture of propane and butane.
Yes, I consider them to be a gas fueled light!
"brianwiese",
I am not taking anyone's side in this, just trying to provide code sections as information.
Regarding the outdoor areas, in
Section 1004.8 Outdoor areas, from the 2006 edition of
the IBC:
Yards, patios, courts and similar outdoor areas accessible to and usable by the building
occupants shall be provided with means of egress as required by this chapter.
The occupant
load of such outdoor areas shall be assigned by the building official in accordance with the
anticipated use. Where outdoor areas are to be used by persons in addition to the occupants
of the building, and the path of egress travel from the outdoor areas passes through the
building, means of egress requirements for the building shall be based on the sum of the
occupant loads of the building plus the outdoor areas.
Exceptions:
1. Outdoor areas used exclusively for service of the building need only have one means
of egress.2. Both outdoor areas associated with Group R-3 and individual dwelling units of
Group R-2.
IMO, some code official in your location will need to assign an Occupancy Group to the
areas in question, or as a whole. From your statements, it sounds as though the Fire
Code Official is saying that all Outoddor Areas are an "A" Occ. Group and therefore, no
tiki torches! As "cda" has asked, ..is there a Building Code Official involved in this
application? If not, who is the Code Official with authority?
.