• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

helloarchitect

Registered User
Joined
May 9, 2016
Messages
4
Location
San Francisco
2013 CBC/IBC for R-3

The way we're reading code in Section 1016 is that the overall Exit Distance is limited to 200 feet. According to Section 1014, the Common Path of Travel is limited to 75 feet. This is in a building with two (2) exits.

Are we missing anything? Thanks in advance!
 
$ $ >

Welcome **helloarchitect** to The Building Codes Forum ! :cool:

Is your bldg. sprinkled ?


< $ $
 
Generally single-family R-3 is exempted by the IBC and governed by the IRC. See section 101.2 in the IBC.
 
& = & = &


**helloarchitect**, ...the Common Path of Travel requirements

come from the `13 CBC, Volume 1, Table 1014.3.......Also, see
Note "e", ...this is for mixed occupancy bldgs.

The maximum Travel Distance comes from Table 1016.2, and Yes,
it is 200 ft. without sprinklers.



& = & = &
 
Thank you! This yields 125 feet of exit access travel, on top of the 75 feet requirement for common egress. 200 feet without sprinklers.
 