Emergency showers, should not be on second floor, which is what the post is about.
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
My reply was too short and left you with the wrong impression; I established with the first response accessible shower needs to be on the accessible level, there were additional questions aside from the accessible shower that were not answered and I meant to add that if an emergency shower is necessary it can be easily rectified by tapping into the eye wash station water supply to a shower head.mark handler said:Emergency showers, should not be on second floor, which is what the post is about.
Thanks for having me do right.righter101 said:Does this mean the building department needs to provide me with a shower since some of the submissions i received are "irriating materials"??
I stopped a TI for an office here awhile back when they proposed the breakroom on the second floor with no access for handicapped employees. They looked at a lift, then moved the breakroom downstairs. They also had to put in accessible bathrooms, existing were under the stairs.mtlogcabin said:Stores got nailed about the break rooms and conference rooms on the second floor a few years back. Owner might want to reconsider placing them on the accessible floor.
Unfortunately, I don't have a copy of the 2009 IBC. But, using the 2010 CBC, my answer would be 'yes'. Section 1103B.1 references Section 1114, Facility Accessibility, Section 1114 B.1.2 - Other Building Components(kitchens are included in this subsection).righter101 said:I may have found it myself. 2009 IBC 1108.2.9 Exception 1 seems to address just this situation.Would this be correct to apply to an employee breakroom with a kitchenette??
I don't quite see that, Righter101 on several levels. 2009 IBC 1108.2.9? Dining areas (at least that what my copy of the commentary has)? Exception 1 deals with mezzanines and it doesn't sound like that applies.righter101 said:I may have found it myself. 2009 IBC 1108.2.9 Exception 1 seems to address just this situation.Would this be correct to apply to an employee breakroom with a kitchenette??
I think we can confuse the issue a bit more. It reads, "assembly areas.....". I believe you can have an assembly area or assembly use, ie. break or conference room, yet be within a "B" occupancy. This is one of those things that has probably been hashed before. I think it is an important distinction. You can have a storage "use or area", but not an S occupancy.Francis Vineyard said:The dining area would have to be considered an assembly use group before going to that section; then it will need to be sprinklered. It's still a business use with the dining/kitchen area under 750 sf or the occupant load under 50.Don’t know UPC but in IPC separate facilities are for required fixtures counted; not emergency showers.
Hope this helps.
Agree same as mixed use occupancies along with the definition of Employee Work Area" and 1108 addressing "specific occupancies" substantiates this conclusion.righter101 said:I think we can confuse the issue a bit more. It reads, "assembly areas.....". I believe you can have an assembly area or assembly use, ie. break or conference room, yet be within a "B" occupancy. This is one of those things that has probably been hashed before. I think it is an important distinction. You can have a storage "use or area", but not an S occupancy.Agree or disagree?
Regardless, i think I can go back to general scoping provisions and use 1103.1, "all elements....." etc.. to require it.
What is your opinion on accessibility for the kitchenette and dining area?mark handler said:Breakrooms and employee restrooms/bathing (shower) rooms are considered common use areas and are required to be fully accessible No matter what floor they are on.
righter101 said:There are several issues with the plans for this project. I think I have grasped the accessibility for showers. The second floor showers are somehow for employee use. Since they do not have an accessbile route to the 2nd floor, they need to provide an accessbile one on the first floor. The issue of an emergency shower will be clarified when I determine if any of the componenets of the process are "irriating", per the UPC. We use 2009 Uniform Plumbing Code, and the CH 29 of the IBC.As far as the employee lunch/break room, I am wondering if I can apply 1108.2.9. You are right, the exception may not be relevant. My question is this, can they have the employee break room on the second floor and not provide an accessible route to it?
I believe 1108.2.9 Dining areas. In dining areas, the total floor area
allotted for seating and tables shall be accessible.
Would apply...?? Am I correct in applying this to an employee eating area with a kitchenette?? If not, is there anything that can require the break room to be accessible>??
Do i just revert back to 1103.1 Sites, buildings, structures, facilities,
elements and spaces, temporary or permanent, shall be accessible
to persons with physical disabilities.
Considered common use areas and agree with Peach on equivalent facilities.Francis Vineyard said:What is your opinion on accessibility for the kitchenette and dining area?
Where exceptions are permitted and are outside the perimeters of ADA are in violation with the "spirit of the law"? I cannot find this in ADA.peach said:If there are equivalent facilities on both floors, you can maybe eliminate the elevator; showers, break rooms, etc need to also be available on the first floor.. or you're in violation of the spirit of the law.
It is in the scoping of the "new" ADAAGFrancis Vineyard said:Where exceptions are permitted and are outside the perimeters of ADA are in violation with the "spirit of the law"? I cannot find this in ADA.