• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Appendix B & C ?

mtlogcabin

SAWHORSE
Joined
Oct 17, 2009
Messages
9,507
Location
Big Sky Country
A question came up in house. A 27,000 sq ft V-B building requires 4500 GPM fire flow for 4 hours.
Table B105.2 permits a 75% reduction in the required fire flow in a sprinkled building which would be 1,125 GPM
Now go to Appendix C for fire hydrants. Do you use the original 4500 GPM or the reduced number of 1,125GPM
The big difference if 5 required hydrants or 1. With 1 hydrant you will be dragging a lot of hose

We have never done it that way but the question came up as to why not?
 