Are sprinklers required for an outdoor assembly area under a metal canopy?

Nearly-Complete

REGISTERED
Joined
Feb 8, 2019
Messages
27
Location
California
If this was enclosed, sprinklers are clearly required: A-2 occupancy with occupant load factor of 15, 1750 square feet, so occupant load of 117 which requires sprinklers per 903.2.1.2.

The architect thinks this does not meet the definition of a fire area. The fire chief does.

I’m in California but it looks like this is model code language:

Ch 2 Definitions:
Building: Any structure used or intended for supporting or sheltering any use or occupancy.

Fire Area: The aggregate floor area enclosed and bounded by fire walls, fire barriers, exterior walls, OR horizontal assemblies of a building. Areas of a building not provided with surrounding walls shall be included in the fire area if such areas are included within the horizontal projection of the roof or floor next above.
 