at the last minute
Oh Well
At the first inspection, I wrote a correction that the service drop is too close to the water. That old style drop must be changed to a triplex and it can then be as close as 12'.
However, Edison will not change the drop unless I release the panel. Well it's not the original equipment and there is no permit for an upgrade.
The pool contractor has his head in the sand.
Where do you see 12'?
It is 22' in 680.8, Supported on and Cabled Together with a Solidly Grounded Bare Messenger or Solidly Grounded Neutral Conductor up to 750v.
Otherwise 25'
gfretwell said:
Where do you see 12'? It is 22' in 680.8, Supported on and Cabled Together with a Solidly Grounded Bare Messenger or Solidly Grounded Neutral Conductor up to 750v.
Otherwise 25'
Here in California, we are forced to let the utility company make the rules.