steveray said:
State law requires FPE design....I require it to be complete or thorough...
I was kind of thinking an overview/detailed review of the project.
If you want to use thier FPE or require an approved third party. Not just design but details of all processes, storage, chemicals and code anyalsis how to protect the place.
104.7.2 Technical assistance. To determine the acceptability
of technologies, processes, products, facilities, materials
and uses attending the design, operation or use of a building
or premises subject to inspection by the fire code official, the
fire code official is authorized to require the owner or agent
to provide, without charge to the jurisdiction, a technical
opinion and report. The opinion and report shall be prepared
by a qualified engineer, specialist, laboratory or fire safety
specialty organization acceptable to the fire code official
and shall analyze the fire safety properties of the design, operation
or use of the building or premises and the facilities
and appurtenances situated thereon, to recommend necessary
changes. The fire code official is authorized to require
design submittals to be prepared by, and bear the stamp of, a
registered design professional.