because I;m holding my cane in the other hand!One of your best responses to date ICE. Thank you
Now please explain why residential stairs only have one handrail in many cases?
because I;m holding my cane in the other hand!One of your best responses to date ICE. Thank you
Now please explain why residential stairs only have one handrail in many cases?
So though we measure the steps nose to nose, that same match point is not used at the landing, and am I reading correctly you choose a point less than 11 but more than zero, so lets say 6"You would measure where the foot will land which will be just in front of the nosing not 11 inches away from the nosing. Only a kid jumping from the upper risers will land that far in front of the nosing of the riser
Yes the way you explained it is exactly the way I understand it to be, there is however an exception to allow the first riser to be less than 4" if the stairs adjoin to a sloped sidewalk I believe. And for your first question I have always measured to point A on your diagram however, logically that may be wrong but I'd rather not fail something unless it's specifically stated in the code.So lets circle back to the note about the 3/8" tolerance.
The way I read this section is as follows.
How do you see the 3/8"?
- You measure all your tread depths and riser heights
- the shortest riser can't be more than 3/8" less than the tallest riser within the flight
- the shortest tread can't be more than 3/8" less than the longest tread within the flight
- Period
- The 3/8" tolerance does not allow for the tallest riser within the flight to exceed the 7" nor reduce the shortest to be less than 4"
- It is a tolerance that is boxed in between the 2 numbers, being the minimum and maximum.
Right, but you missed the point of the question. Suppose the sidewalk or ground slopes. If you measure right at the edge of the next step, you get 7" and all is well. But if you measure out at the end of the imaginary step ... 11" away ... you could get 9" rise. Look at the sketch in post 6.Here, code stipulates it is top of tread or landing to top of tread or landing.
Landing area has to be flat. Otherwise it is a ramp. Code does not allow stairs to terminate to a ramp. You can do stairs to a leading to a ramp, but not stairs directly to a ramp... At least here in this crazy country.Right, but you missed the point of the question. Suppose the sidewalk or ground slopes. If you measure right at the edge of the next step, you get 7" and all is well. But if you measure out at the end of the imaginary step ... 11" away ... you could get 9" rise. Look at the sketch in post 6.
What do you do for deck stairs that land on uneven ground? No tolerance for natural slope?Landing area has to be flat. Otherwise it is a ramp. Code does not allow stairs to terminate to a ramp. You can do stairs to a leading to a ramp, but not stairs directly to a ramp... At least here in this crazy country.
A landing is not required for stairs serving a single dwelling unit, so we would just measure right in front of the nosing. For any other occupancy, a landing is required and would need to be flat.What do you do for deck stairs that land on uneven ground? No tolerance for natural slope?
Does not the code have the same restriction for slope on treads and landings, thus per your reason, why are treads measured nose to nose?Landing area has to be flat. Otherwise it is a ramp. Code does not allow stairs to terminate to a ramp. You can do stairs to a leading to a ramp, but not stairs directly to a ramp... At least here in this crazy country.
Fail. The TOS is a maximum, not a defined dimension. The contractor should have installed at 33-3/4 to allow for typical construction conditions.Consider a 24" deep sink counter in a RR with a 2% slope from the back wall to a floor drain. it is 34" max. T. O.S. at the wall but (+) 34" 2' out, is that a violation or an allowed tolerance?
Is my code book missing an exception for bottom landings for a single dwelling?A landing is not required for stairs serving a single dwelling unit, so we would just measure right in front of the nosing. For any other occupancy, a landing is required and would need to be flat.
I use a different code book than you folks.Is my code book missing an exception for bottom landings for a single dwelling?
2015 IBC:
1011.6 Stairway landings. There shall be a floor or landing
at the top and bottom of each stairway. The width of landings
shall be not less than the width of stairways served. Every
landing shall have a minimum width measured perpendicular
to the direction of travel equal to the width of the stairway.
Where the stairway has a straight run the depth need not
exceed 48 inches (1219 mm). Doors opening onto a landing
shall not reduce the landing to less than one-half the required
width. When fully open, the door shall not project more than
7 inches (178 mm) into a landing. Where wheelchair spaces
are required on the stairway landing in accordance with Section
1009.6.3, the wheelchair space shall not be located in the
required width of the landing and doors shall not swing over
the wheelchair spaces.
Exception: Where stairways connect stepped aisles to
cross aisles or concourses, stairway landings are not
required at the transition between stairways and stepped
aisles constructed in accordance with Section 1029.
Code says you need a landing or a floor. So no landing is required if there is a floor?
I don't disagree with you that this creates consistency with how the remainder of the stairs are measured. However, as a building official I am not given any guidance on how to measure the rise height from a landing to the first tread, so I do it the easiest way possible for me. If someone wanted to push the issue and demonstrate that stairs that I found non-compliant met compliance when measured the way you advocate for, I would be amenable to this solution.Does not the code have the same restriction for slope on treads and landings, thus per your reason, why are treads measured nose to nose?
As to the landing being not sloped, in a perfect world, not only are they not sloped, but they are also inspected correctly.
Thus the circle around, why aren't the bottom risers measured 1 tread depth out?
Is my code book missing an exception for bottom landings for a single dwelling?
2015 IBC:
1011.6 Stairway landings. There shall be a floor or landing
at the top and bottom of each stairway. The width of landings
shall be not less than the width of stairways served. Every
landing shall have a minimum width measured perpendicular
to the direction of travel equal to the width of the stairway.
Where the stairway has a straight run the depth need not
exceed 48 inches (1219 mm). Doors opening onto a landing
shall not reduce the landing to less than one-half the required
width. When fully open, the door shall not project more than
7 inches (178 mm) into a landing. Where wheelchair spaces
are required on the stairway landing in accordance with Section
1009.6.3, the wheelchair space shall not be located in the
required width of the landing and doors shall not swing over
the wheelchair spaces.
Exception: Where stairways connect stepped aisles to
cross aisles or concourses, stairway landings are not
required at the transition between stairways and stepped
aisles constructed in accordance with Section 1029.
Code says you need a landing or a floor. So no landing is required if there is a floor?
A northern version I suspect!I use a different code book than you folks.
I don't think I said anything about a door and I thought we were on the IBCYou are correct if using the IBC for egress. the question on the deck stairs was for residential. The IRC only requires one egress door from a home and that is usually the front door.
This was in response to your stair landing post. Chapter 10 is for egress in the IBC. Was only pointing out this is not in the IRC. A landing is not required for deck steps and such. I still measure for the consistency and here in NM you can have 8" rise and 9" tread in the adopted code. I would measure from the nose of the last step to the ground, landing, pavers ect.you are correct if using the IBC for egress. the question on the deck stairs was for residential. The IRC only requires one egress door from a home and that is usually the front door.
I don't think I said anything about a door and I thought we were on the