UGH!UPC I believe has different ways (OL) for fixture count....I believe the Cali folks taught me that....If the BO's really want to be jerks, the waiting room is really 7 per (chairs not fixed)
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
UGH!UPC I believe has different ways (OL) for fixture count....I believe the Cali folks taught me that....If the BO's really want to be jerks, the waiting room is really 7 per (chairs not fixed)
I agree with you. Looking for some negotiation room but, we are dealing with a third party reviewer so we're not going to get anywhere with them. We'll have to talk directly with the AHJ. Seeing our firm will be doing numerous installation like this I want to make sure we approach each project correctly. Of course the client won't like the increase in fixtures.
I seemed to have missed where the OP said this project was in CA.In CA minimum fixture requirements are based upon occupant load calculation from the plumbing code and are separate from occupant load for exiting calculations.
I was just saying there are two different occupant loads for exiting and plumbing purposes in CA. No idea where he is but seems like perhaps IBC.I seemed to have missed where the OP said this project was in CA.
I agree with you. Looking for some negotiation room but, we are dealing with a third party reviewer so we're not going to get anywhere with them. We'll have to talk directly with the AHJ. Seeing our firm will be doing numerous installation like this I want to make sure we approach each project correctly. Of course the client won't like the increase in fixtures.
Nope. A toilet and urinal in a single occupant room only count as one.As far as fixture count, you do not "double count" unisex......Do you?
Nope. A toilet and urinal in a single occupant room only count as one.
Nope. A toilet and urinal in a single occupant room only count as one.
That is presumptive in this day & age....
I am not sure I can get behind that, on many occasions I have seen every seat in the waiting room of my doctors office filled, with people standing / waiting against the walls, with an additional group of people waiting in line to check in. And a lot of those people will be waiting in that room for 45 minutes to an hour.I count the number of seats in the waiting room and use that in lieu of 15 sq ft pp OL
Remember gross OL does not include the exterior walls
I am not sure I can get behind that, on many occasions I have seen every seat in the waiting room of my doctors office filled, with people standing / waiting against the walls, with an additional group of people waiting in line to check in. And a lot of those people will be waiting in that room for 45 minutes to an hour.
IBC. Clinic is 1/100.Are you on the IPC or UPC?
also, with calculating the waiting room at 1 per 15, the storage & mechanical spaces at 1 per 300 & the remaing clinic area at 1 per 150 (or 1 per 100 depending on what version of the IBC your on) how many occupants do you come up with for each of the 3 occupant load calculations?
This project happens to be in Arizona.I seemed to have missed where the OP said this project was in CA.
could you ask for a code mod to use the 2018 IBC to calculate the office area occupant loads at 1 person per 150SFIBC. Clinic is 1/100.
Interesting. I'll look this over.I am not sure you need to do anything to your plumbing counts assuming you current show (1) make & (1) female toilet room. Looking back thru your posts you have a 3300 SF clinic with a 479 SF waiting area. Based on that info I am coming up with 32 occupants in the waiting area (479 / 15) & 29 occupants in the remainder of the building (2821 / 100) . I then apply the B occupancy plumbing calculations to the 29 occupants and one of the A3 Occupancy plumbing calculations to the 32 waiting room occupants. Even though the waiting room is technical a B occupancy and not an A3 occupancy, the IPC code commentary is very clear that plumbing fixtures can be calculated this way.
If we are all in agreement with this, I then come up with the following calculations
Water Closets
A3 Male water closets 1 per 125 = 0.13 fixtures
B Male water closets = 0.60 fixtures
Total male water closets = 0.73, rounded up to 1.0
A3 Female water closets 1 per 65 = 0.25 fixtures
B Female water closets = 0.60 fixtures
Total Female water closets = 0.85, rounded up to 1.0
Lavatories
A3 Male lavatories 1 per 200 = 0.08 fixtures
B Male lavatories = 0.38 fixtures
Total male lavatories = 0.46, rounded up to 1.0
A3 Female lavatories 1 per 200 = 0.08 fixtures
B Female lavatories = 0.38 fixtures
Total Female lavatories = 0.46, rounded up to 1.0
Drinking Fountains
A3 Drinking Fountains 1 per 500 = 0.06
B Drinking Fountains 1 per 100 = .29
Total Drinking Fountains = 0.35, rounded up to 1……(Must provide a high & low fixture, minimum of 2 DF required)
So based on my math you need to provide one male and one female toilet room, and 2 drinking fountains to meet the HiLo Requirement
What happened during plan check? Was it approved with just two toilets?Interesting. I'll look this over.
Can you direct me to the code exception that allows to break the occupant load calculations?I am not sure you need to do anything to your plumbing counts assuming you current show (1) make & (1) female toilet room. Looking back thru your posts you have a 3300 SF clinic with a 479 SF waiting area. Based on that info I am coming up with 32 occupants in the waiting area (479 / 15) & 29 occupants in the remainder of the building (2821 / 100) . I then apply the B occupancy plumbing calculations to the 29 occupants and one of the A3 Occupancy plumbing calculations to the 32 waiting room occupants. Even though the waiting room is technical a B occupancy and not an A3 occupancy, the IPC code commentary is very clear that plumbing fixtures can be calculated this way.
If we are all in agreement with this, I then come up with the following calculations
Water Closets
A3 Male water closets 1 per 125 = 0.13 fixtures
B Male water closets = 0.60 fixtures
Total male water closets = 0.73, rounded up to 1.0
A3 Female water closets 1 per 65 = 0.25 fixtures
B Female water closets = 0.60 fixtures
Total Female water closets = 0.85, rounded up to 1.0
Lavatories
A3 Male lavatories 1 per 200 = 0.08 fixtures
B Male lavatories = 0.38 fixtures
Total male lavatories = 0.46, rounded up to 1.0
A3 Female lavatories 1 per 200 = 0.08 fixtures
B Female lavatories = 0.38 fixtures
Total Female lavatories = 0.46, rounded up to 1.0
Drinking Fountains
A3 Drinking Fountains 1 per 500 = 0.06
B Drinking Fountains 1 per 100 = .29
Total Drinking Fountains = 0.35, rounded up to 1……(Must provide a high & low fixture, minimum of 2 DF required)
So based on my math you need to provide one male and one female toilet room, and 2 drinking fountains to meet the HiLo Requirement
I agree the Occupant load should be calculated at 1/15 unless you have a furniture layout that would show otherwise. But in any case you should not be using Assembly anything for the plumbing calcs. it is all B.In this case I'm with the BO, the waiting room should be calculated at 1 person per 15SF