I have a question that I believe will garner different answers.
If I have a new building with a new electrical service and prior to pouring the foundation, a code-compliant connection of a properly sized Grounding Electrode Conductor (GEC) to the rebar in the footing is made that connects the GEC to hundreds of feet of #4 rebar, is a ground rod(s) even necessary?
I will say that I often see a triangle of 10' ground rods for the Grounding Electrode System (GES) in addition to hitting building steel such as footing rebar, but are the ground rods even necessary to comply with the code at that point?
If I have a new building with a new electrical service and prior to pouring the foundation, a code-compliant connection of a properly sized Grounding Electrode Conductor (GEC) to the rebar in the footing is made that connects the GEC to hundreds of feet of #4 rebar, is a ground rod(s) even necessary?
I will say that I often see a triangle of 10' ground rods for the Grounding Electrode System (GES) in addition to hitting building steel such as footing rebar, but are the ground rods even necessary to comply with the code at that point?