2012 International Codes. We have a building containing 4,696 sq. ft. and was converted from a Mercantile occupancy to an A2 occupancy (night club) back in 2010. The structure was required to install an NFPA 13 sprinkler system. Since then the night club failed and now the structure is being converted to a Business occupancy. The lessee and owner are claiming that the sprinkler system is no longer required. While a typical Business occupancy of this size would not require a sprinkler system, I & the Fire Department can not find any thing in the codes that allow for the shut down of this system (stop monitoring, drain the system but not remove it, no more yearly inspections).
Would this be allowed? Need code references that would allow for the shut down of the sprinkler system (if they exist).
Thanks
IFC
901.6 Inspection, testing and maintenance. Fire detection, alarm and extinguishing systems shall be maintained in an operative condition at all times, and shall be replaced or repaired where defective. Nonrequired fire protection systems and equipment shall be inspected, tested and maintained or removed.
Fire departments do not like to do it but it can be done under the IFC.
901.7 Systems out of service.
Where a required fire protection system is out of service, the fire department and the fire code official shall be notified immediately and, where required by the fire code official, the building shall either be evacuated or an approved fire watch shall be provided for all occupants left unprotected by the shutdown until the fire protection system has been returned to service.
Where utilized, fire watches shall be provided with at least one approved means for notification of the fire department and their only duty shall be to perform constant patrols of the protected premises and keep watch for fires.
901.7.1 Impairment coordinator.
The building owner shall assign an impairment coordinator to comply with the requirements of this section. In the absence of a specific designee, the owner shall be considered the impairment coordinator.
901.7.2 Tag required.
A tag shall be used to indicate that a system, or portion thereof, has been removed from service.
901.7.3 Placement of tag.
The tag shall be posted at each fire department connection, system control valve, fire alarm control unit, fire alarm annunciator and fire command center, indicating which system, or part thereof, has been removed from service. The fire code official shall specify where the tag is to be placed.
901.7.4 Preplanned impairment programs.
Preplanned impairments shall be authorized by the impairment coordinator. Before authorization is given, a designated individual shall be responsible for verifying that all of the following procedures have been implemented:
1. The extent and expected duration of the impairment have been determined.
2. The areas or buildings involved have been inspected and the increased risks determined.
3. Recommendations have been submitted to management or building owner/manager.
4. The fire department has been notified.
5. The insurance carrier, the alarm company, building owner/manager, and other authorities having jurisdiction have been notified.
6. The supervisors in the areas to be affected have been notified.
7. A tag impairment system has been implemented.
8. Necessary tools and materials have been assembled on the impairment site.
mtlogcabin said:
Fire departments do not like to do it but it can be done under the IFC.901.7 Systems out of service.
I take this section to be used fortemporary out of service, not for ever and ever
cda said:
I take this section to be used for temporary out of service, not for ever and ever
Most Fire Officials agree with you. So you make someone spend the money to remove a system in lieu of following a code procedure that makes sense.
We had a previous FO that required the drops/heads and FDC, in lieu of the entire system, be removed in one building that went from an I-4 to office.
mtlogcabin said:
Most Fire Officials agree with you. So you make someone spend the money to remove a system in lieu of following a code procedure that makes sense.We had a previous FO that required the drops/heads and FDC, in lieu of the entire system, be removed in one building that went from an I-4 to office.
Code says this also:: Nonrequired fire protection systems and equipment shall be inspected, tested and maintained or removed.
Some people think iof they see a fire sprinkler head or smoke detector, that they work,
And have a warm fuzzy feeling knowing they are better protected.
I did not find anything in the code requiring warm fuzzy feelings or as the commentary states "avoid creating a false impression of adequate protection"
Who is the commentator concerned about having a false sense? The building owner? The fire fighters? The general public/employees who can't tell if sprinkler system is installed if concealed heads are used?
By following Section 901.7 everyone who needs to know the system is non-functional knows. If the system is brought back into service 901.7.6 specifies certain requirements.
1 or 2 years later the business moves out and an A-2 use comes back in.
901.6 Sounds like a code provision to keep the sprinkler installers employed
What was and is no longer, need not be left to create false impressions to the unknowing.
To leave it in place allows the potential for any fire insurance carrier to deny any future claim and to question any and all work associated with the change in occupancy (assuming no permits were pulled).
Disagree
The insurance carrier will raise the rates accordingly for a non-sprinklered building
cda said:
My first actual position would be to tell them to keep it active and maintain it
I agree and would guess that would be the majority opinion on this board.
The maintain or remove portion in the code sound almost like intimidation tactics the mob would use.
Greetings,
I am just an old ditch digging electrician. But I do the fire thing part time and know a lot of fire dudes. Several have told me over the years that you never want to have life safety type of equipment in place and not have it maintained because you never want to give folks a false sense of security. Makes sense. Code says maintain if it's there. I say remove it completely if no longer required and maintained.
Byron
Frank said:
Remove the visible sprinkler heads and the FDC. Abandon the rest in place. Intent of code is met.
Agreed. The last thing anyone wants is to assume the sprinklers are in working order when they are not.
Well.....kinda, but not really.........there are two camps, keep it, or remove all visible portions.........I'm with the remove visible portions, but would advise retaining it for possible future uses.
mtlogcabin said:
I did not find anything in the code requiring warm fuzzy feelings or as the commentary states "avoid creating a false impression of adequate protection"Who is the commentator concerned about having a false sense? The building owner? The fire fighters? The general public/employees who can't tell if sprinkler system is installed if concealed heads are used?
I think this would apply to the "warm and fuzzy" part...
901.4.5 Appearance of equipment.
Any device that has the physical appearance of life safety or fire protection equipment but that does not perform that life safety or fire protection function shall be prohibited.
It is permitted and recognized by the referenced standard therefore since an existing system is not required by the driving code for the change of occupancy the system may be abandoned provided it is done so by the referenced installation standard. The occupancy change does not require protection in accordance with IEBC therefore the owner may apply the following:
[iBC 2012 901.1] Scope. The provisions of this chapter shall specify where fire protection systems are required and shall apply to the design, installation and operation of fire protection systems.
[iFC 2012 901.1] Scope. The provisions of this chapter shall specify where fire protection systems are required and shall apply to the design, installation, inspection, operation, testing and maintenance of all fire protection systems.
NFPA 13, 2010 (As Referenced)
26.2* Inactive Sprinkler SystemsAbandoned in Place.
26.2.1 Where all or part of an inactive sprinkler system is abandoned in place, components including sprinklers, hose valves and hoses, and alarm devices shall be removed.
26.2.2 Control valves abandoned in place shall have the operating mechanisms removed.
26.2.3 Sprinkler system piping and/or valves abandoned in place shall be uniquely identified to differentiate them from active system piping and valves.
A.26.2 The presence of a sprinkler system and components creates a reasonable expectation by the public that these safety features are functional. When systems are inoperable or taken out of service but the devices remain, they present a false sense of safety. Also, before taking any part of a sprinkler system out of service, extreme care needs to be exercised to ensure that the system is not required, was not originally provided as an alternative or equivalent, or is no longer required due to other new requirements in the current codes and standards. It is not intended that the entire system or all components be removed. Instead, components such as sprinklers, initiating devices, notification appliances, and standpipe hose should be removed to reduce the likelihood of relying on inoperable systems or features. Control valves and other components that are allowed to be abandoned in place should have operating mechanisms removed and be painted a unique color to indicate that they are no longer in service.
Is it a good idea? (No)
Is it permitted by a building owner? (Yes)
I still contend that the vast majority of the public have no idea of when they are in a sprinklered building or not and therefore the above quote is a false assumption