Re: College dormitory "lounges" open to the rated exit corridor
texasbo said:
Gene Boecker said:
I have to disagree.What prevents them from being IN the corridor?
There's text to prohibit stuff from being the the exits but there's nothing prohibiting stuff from being in the corridor.
In my opinion, 1017.5, Corridor continuity, prevents them from being IN the corridor.
I agree with CDA and others who say: if you allow this, why not allow other rooms; toilet rooms, storage rooms, break rooms, janitor's closet? Pretty soon you've got everything but the kitchen sink being called part of the corridor, and in my opinion that violates the intent and the letter (1017.5) of the code.
However, in this particular case, I agree with Daves and think the lounge is the same as a foyer, reception area or lobby, and if constructed as required for a corridor would qualify for the exception in 1017.5.
I've been approached numerous times by numerous man with pencil requesting toilet rooms, break rooms, vending rooms, etc to not be separated from the fire resistance rated corridor. That is a violation. If fire resistance rating is required, a corridor is a corridor, and a room is a room, and the two must be separated, with the only exceptions being foyers, lobbies, reception rooms.
So? When was the last time a vending machine burned down a building and killed people (I mean OTHER than by what was consumed - lol)? I'd lump that in with lobby/reception are/foyer. Ditto with the toilet room. They may be considered a hazardous waste facility but not highly combustible.