• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Compliant with NEC 250.24(A)(1)

jar546

Forum Coordinator
Joined
Oct 16, 2009
Messages
11,092
Location
Somewhere Too Hot & Humid
As you can see by this photograph, the grounding electrode conductor (GEC) for this service comes into the top of the panel on the meter-base side and connects to a lug that is mechanically connected to a factory installed strip of metal that then connects the ground lug where the service neutral is also connected. That factory installed metal strip also connects the ground bar for the load side neutral connection and is bonded to the enclosure. This would be an acceptable location to connect the GEC under NEC 240.24(A)(1)

Do you agree?

IMG_5494.JPG
 