All, need a little help, when is nm cable required to be in conduit in a commercial setting, code sections would be very helpful. CEC.
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
The code used to allow "or other approved means". I don't have a copy with me but if that's still the case, then NM isn't required to be in conduit anywhere in the NEC.north star said:+ & + & +
Chad,
Not sure of the CEC Articles, but in the `14 Edition of the NEC,
Article 334.12(B) requires NM to be in conduit to provide "protection
from physical damage".
+ & + & +
I have heard about the union conduit rule in some areasnorth star said:+ & + & +
Chad,
Not sure of the CEC Articles, but in the `14 Edition of the NEC,
Article 334.12(B) requires NM to be in conduit to provide "protection
from physical damage".
As **cda** mentioned, the AHJ may have some type of requirement
in their Ordinances.........Recommend that you contact the AHJ in
question and ask for specifics.
+ & + & +