All, need a little help, when is nm cable required to be in conduit in a commercial setting, code sections would be very helpful. CEC.
The code used to allow "or other approved means". I don't have a copy with me but if that's still the case, then NM isn't required to be in conduit anywhere in the NEC.north star said:+ & + & +
Chad,
Not sure of the CEC Articles, but in the `14 Edition of the NEC,
Article 334.12(B) requires NM to be in conduit to provide "protection
from physical damage".
+ & + & +
I have heard about the union conduit rule in some areasnorth star said:+ & + & +
Chad,
Not sure of the CEC Articles, but in the `14 Edition of the NEC,
Article 334.12(B) requires NM to be in conduit to provide "protection
from physical damage".
As **cda** mentioned, the AHJ may have some type of requirement
in their Ordinances.........Recommend that you contact the AHJ in
question and ask for specifics.
+ & + & +