I have a proposed access control set-up I need help with. The first submittal was for mag-lock door, installed in a 1-hr fire barrier. It was shown as a glass door. I sent it back, requesting a rated opening and active latch bolt and closer. The response was to provide a 1-hr SC wood door, with a mag-lock, and a levered handle that provided a positive latch. They are providing a sensor release on the interior, with a push to exit as a secondary release, and interruption of power to the magnet if loss of power, sprinkler or alarm activation. These requirements are straight out of the book for 2012 IBC 1008.1.9.8 access controlled egress doors, which does not appear to include mag-locks. Mag-locks, as covered by 1008.1.9.9 require listed hardware with a built in switch. It seems as though they are combining the two sections. So the sequence of operations is this:
From the inside, approach the door, a sensor detects and release the mag-lock, you then operate the lever handle. As a secondary, if the sensor does not detect, you push the manual unlocking device, then operate the lever.
In both cases, the hardware is free egress, and the door remains latched.
If this makes any sense, is it compliant? Lori, are you out there?