Can i have an interconnecting stair within a control area, that is open between just the two floors?
CBC and CFC simply say that control areas need to be separated by fire barriers(CBC707) and/or horizontal assemblies (CBC 711). There are no other requirements out of CBC 414 or CFC 5003 regarding vertical openings in control areas. CBC 712.9 does not list control areas as a restriction for two-story open stairways.
CBC and CFC simply say that control areas need to be separated by fire barriers(CBC707) and/or horizontal assemblies (CBC 711). There are no other requirements out of CBC 414 or CFC 5003 regarding vertical openings in control areas. CBC 712.9 does not list control areas as a restriction for two-story open stairways.