gelarehg@CotamDesign
Hi all,
I'm working on an ADU and came across a problem. there are existing 2x6 ceiling joists i and need to change them to a one hour fire rated ceiling assembly. Project is located in California. Some of the joists are 2x6 and some are 2x10, even though in the code it doesn't say the size of the joists and it just says 16 oc, but the plan checker asked to have 2x10 joists. I can sister up the 2x10 to the existing 2x6, and add more where I don't have them 16" oc. I reviewed chapter 7 On table 722.6.2 (1), adding Gyp Board Type "x" gives me 40 mins. On table 722.6.2(2) it says wood floor joists @16" oc gives me 15 mins. I'm still short by 5 mins. On table 722.6.2(5) it says "if the spaces between the studs are completely filled with glass fiber mineral wool batts weighing not less than 2 pounds per cubic foot (0.6 pound per square foot of wall surface) or rockwool or slag material wool batts weighing not less than 3.3 pounds per cubic foot (1 pound per square foot of wall surface), or cellulose insulation having a nominal density not less than 2.6 pounds per cubic foot."
I already have R-19 batt per energy calcs. Anybody can advice me how to make this change happen? can I use any of the insulation options in leu of R-19? Or any idea?