• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

CPC Shower stall

ICE

Oh Well
Staff member
Joined
Jun 23, 2011
Messages
12,902
Location
California
408.6 Shower Compartments. Shower compartments, regardless of shape, shall have a minimum finished interior
1024 square inches and shall also be capable of encompassing a 30 inch circle. The minimum required area and dimensions shall be measured at a height equal to the top of the threshold and a point tangent to its center-line. The area and dimensions shall be maintained to a point of not less than 70 inches above the shower drain outlet with no protrusions other than the fixture valve or valves, shower heads, soap dishes, shelves, and safety grab bars, or rails. Fold-down seats in accessible shower stalls shall be permitted to protrude into the 30 inch circle.

Exception #2
The minimum required area and dimension shall not apply for a shower receptor having overall dimensions of not less than 30 inches (762 mm) in width and 60 inches (1524 mm) in length.


The job is a hotel bathroom that is being remodeled ....times a few hundred. As the picture shows, the outside dimension of the prefabricated shower enclosure as measured at the dam is 29.125". There will be a glass door which will line up with the center of the dam. The net dimension of the compartment will be 27.5". The long dimension of the compartment is 60".

The argument being made is that because the manufacturer lists this shower as 30"x60", exception #2 applies. The word overall in reference to the receptor is key. If the inside of the receptor were in fact 30"x60" there would not be an issue as the compartment would by default meet code. Hence the assumption that the outer dimension is the "overall". I suppose that one would then be required to measure to the outer edged of the back wall of the enclosure.

However, It seems odd that the exception exists at all.

IMG_2997.jpeg
 
accepted industry standard due to rough framing?
This is a prefabricated fiberglass one piece shower compartment. One of our engineers theorized that the exception is a nod to the replacement of bathtubs with showers in the same space.
 
Last edited:
This is a prefabricated fiberglass one piece shower compartment. One of our engineers theorized that the exception is a nod to the replacement of bathtubs with showers in the same space.
walls of unit thicker then the C.I. tub?
 