I don’t think you’re going to find an exception, A117.1 doesn’t say anything about parallel curb ramps that I can find.Looking for an exception for a ramp curb on these two ramps and the top landings.
I agree it would seem odd, but it’s also odd to not have the edge protection on a ramp. Here’s an article with several illustrations of parallel curb ramps, see Section 6.6, not one has edge protection between the ramp and the road:Don't seem right to put a 4" curb on top of the curb.
A117.1 402.2 does list curb ramps and ramps as separate components of an accessible route:Curb ramps are not ramps....
Plus there are two separate sections as steveray pointed out:A117.1-2009 402.2 Components (Excerpt)
Accessible routes shall consist of one or more of the following components: Walking surfaces with a slope not steeper than 1:20, doors and doorways, ramps, curb ramps excluding the flared sides…
406 is curb ramps....no? 405 IS ramps
In my state I am required to go exactly as the ICC/ANSI A117.1-2006 section 405.9 says.
Now that I look more closely at 406.1 I guess that because it doesn’t say that we have to comply with 405.8 Handrails or 405.9 Edge Protection that curb ramps don’t need to have handrails or edge protection.A117.1-2009 406.1 General [Names of sections added.]
Curb ramps on accessible routes shall comply with Sections 406, 405.2 [Slope], 405.3 [Cross Slope], and 405.10 [Wet Conditions].
Looking for an exception for a ramp curb
I was mistaken to think that A117.1 has to specifically address parallel curb ramps. I think your “exception” is 406.1 because it doesn’t state that you need edge protection on curb ramps.I don’t think you’re going to find an exception, A117.1 doesn’t say anything about parallel curb ramps that I can find.
This looks legal to me. Another design could include stopping the sidewalk that comes in at the right 30 feet from the curb ramp. The landing above the curb ramp goes away. In place of the landing could be a ramp from the curb ramp to the FF of the covered walkway.View attachment 13824
Looking for an exception for a ramp curb on these two ramps and the top landings. Don't seem right to put a 4" curb on top of the curb.
A117.1 402.2 does list curb ramps and ramps as separate components of an accessible route:
Plus there are two separate sections as steveray pointed out:
Now that I look more closely at 406.1 I guess that because it doesn’t say that we have to comply with 405.8 Handrails or 405.9 Edge Protection that curb ramps don’t need to have handrails or edge protection.
I was mistaken to think that A117.1 has to specifically address parallel curb ramps. I think your “exception” is 406.1 because it doesn’t state that you need edge protection on curb ramps.
You’re welcome. When I think “curb ramp” I automatically think of flared sides, parallel curb ramps to me seem like two “regular” ramps.i never thought to call it a curb ramp because to me it does not look like me without the flared sides. But I see the flare sides are not required and there is no definition of curb ramps so I can assume it is a curb ramp. Thanks Walker T.