Curb on top of a curb?

Looking for an exception for a ramp curb on these two ramps and the top landings.
I don’t think you’re going to find an exception, A117.1 doesn’t say anything about parallel curb ramps that I can find.

The U.S. Access Board must consider this an unstated exception to the need for edge protection, they show a parallel curb ramp without edge protection in this animation (link is cued up to the part showing the parallel curb ramp):



Don't seem right to put a 4" curb on top of the curb.
I agree it would seem odd, but it’s also odd to not have the edge protection on a ramp. Here’s an article with several illustrations of parallel curb ramps, see Section 6.6, not one has edge protection between the ramp and the road:

 
In my state I am required to go exactly as the ICC/ANSI A117.1-2006 section 405.9 says. Looks like i will tell them to put in the required curbs on top of the curbs for the ramps and the top landings or they can appeal.
 
Curb ramps are not ramps....
A117.1 402.2 does list curb ramps and ramps as separate components of an accessible route:
A117.1-2009 402.2 Components (Excerpt)
Accessible routes shall consist of one or more of the following components: Walking surfaces with a slope not steeper than 1:20, doors and doorways, ramps, curb ramps excluding the flared sides…
Plus there are two separate sections as steveray pointed out:
406 is curb ramps....no? 405 IS ramps

In my state I am required to go exactly as the ICC/ANSI A117.1-2006 section 405.9 says.
A117.1-2009 406.1 General [Names of sections added.]
Curb ramps on accessible routes shall comply with Sections 406, 405.2 [Slope], 405.3 [Cross Slope], and 405.10 [Wet Conditions].
Now that I look more closely at 406.1 I guess that because it doesn’t say that we have to comply with 405.8 Handrails or 405.9 Edge Protection that curb ramps don’t need to have handrails or edge protection.

Looking for an exception for a ramp curb
I don’t think you’re going to find an exception, A117.1 doesn’t say anything about parallel curb ramps that I can find.
I was mistaken to think that A117.1 has to specifically address parallel curb ramps. I think your “exception” is 406.1 because it doesn’t state that you need edge protection on curb ramps.
 
View attachment 13824

Looking for an exception for a ramp curb on these two ramps and the top landings. Don't seem right to put a 4" curb on top of the curb.
This looks legal to me. Another design could include stopping the sidewalk that comes in at the right 30 feet from the curb ramp. The landing above the curb ramp goes away. In place of the landing could be a ramp from the curb ramp to the FF of the covered walkway.
 
A117.1 402.2 does list curb ramps and ramps as separate components of an accessible route:

Plus there are two separate sections as steveray pointed out:




Now that I look more closely at 406.1 I guess that because it doesn’t say that we have to comply with 405.8 Handrails or 405.9 Edge Protection that curb ramps don’t need to have handrails or edge protection.



I was mistaken to think that A117.1 has to specifically address parallel curb ramps. I think your “exception” is 406.1 because it doesn’t state that you need edge protection on curb ramps.

i never thought to call it a curb ramp because to me it does not look like me without the flared sides. But I see the flare sides are not required and there is no definition of curb ramps so I can assume it is a curb ramp. Thanks Walker T.
 
i never thought to call it a curb ramp because to me it does not look like me without the flared sides. But I see the flare sides are not required and there is no definition of curb ramps so I can assume it is a curb ramp. Thanks Walker T.
You’re welcome. When I think “curb ramp” I automatically think of flared sides, parallel curb ramps to me seem like two “regular” ramps.

Unrelated to your question, looking more closely at your photograph, it looks like the asphalt might be sloped up to the striped accessible route marker. That got me wondering how long the run would be for 1:20 sloped walking surfaces, the sketch below shows 60” runs if the lower 3” is made by the asphalt and the rest by sloped walking surfaces. With maximum 1:20 slopes the term “ramp” doesn’t even come into play.