1. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice
Does an Alteration trigger the need for path to street?
Discussion in 'Accessibility' started by nealderidder, Oct 8, 2019.
  1. nealderidder
    nealderidder Bronze Member
    Dec 7, 2010
    196
    9
    I'm working on a TI in an existing building. It's a big TI, includes the entire two floors of the building. This is in California.
    CBC 11B-206.2.1 calls for an accessible route from the building to the street. It notes "at least one".
    CBC 11B-202.4 tells me that in an alteration I'm only required to provide a path of travel to altered elements from the primary entrance to the building. It would appear that my TI wouldn't trigger the need for an accessible route to the street. Am I right?
  2. ADAguy
    ADAguy Registered User
    Sep 11, 2013
    4,532
    431
    If not, then how is one to approach and enter the building if not by an accessible POT? especially if the building is not presently served by one?
    (there I go being logical?)
  3. JPohling
    JPohling Sawhorse
    Aug 16, 2011
    1,149
    149
    That POT from the public sidewalk is often not achievable in an existing building that was constructed prior to this requirement. Is this a change in use? You will need to provide a compliant POT from the accessible parking area serving your suite.
  4. mark handler
    mark handler Sawhorse
    Oct 25, 2009
    10,658
    901
    11B-202.4 Path of travel requirements in alterations, additions and structural repairs
    When alterations or additions are made to existing buildings or facilities, an accessible path of travel to the specific area of alteration or addition shall be provided.
    The primary accessible path of travel shall include:
    1. A primary entrance to the building or facility,
    2. Toilet and bathing facilities serving the area,
    3. Drinking fountains serving the area,
    4. Public telephones serving the area, and
    5. Signs.
    Chapter 2 Definitions
    PATH OF TRAVEL. An identifiable accessible route within an existing site, building or facility by means of which a particular area may be approached, entered and exited, and which connects a particular area with an exterior approach (including sidewalks, streets and parking areas), an entrance to the facility, and other parts of the facility. When alterations, structural repairs or additions are made to existing buildings or facilities, the term “path of travel” also includes the toilet and bathing facilities, telephones, drinking fountains and signs serving the area of work.
  5. mark handler
    Oct 25, 2009
    10,658
    901
    Technically infeasible. In alterations, where the enforcing authority determines compliance with applicable requirements is technically infeasible, the alteration shall provide equivalent facilitation or comply with the requirements to the maximum extent feasible. The details of the finding that full compliance with the requirements is technically infeasible shall be recorded and entered into the files of the enforcing agency.
  6. JPohling
    JPohling Sawhorse
    Aug 16, 2011
    1,149
    149
    In California I have also used 11B-206.2.1 exception 2. "An accessible route shall not be required between site arrival points and the building or facility entrance if the only means of access between them is a vehicular way not providing pedestrian access."
    mark handler likes this.
  7. mark handler
    Oct 25, 2009
    10,658
    901
    But if there is any pedestrian access, Accessible or not, you can not use this.
  8. Yikes
    Yikes Gold Member
    Nov 2, 2009
    1,591
    201
    I have a related question. I am doing a T.I for a religious organization in California on a project that has its own parking garage. It was approved by the AHJ 10 years ago with two accessible stalls, but only the van stall has a POT that does not go behind another vehicle; the other accessible stall goes behind the van stall.
    Q: Since I can comply with POT for all things except access stall #2, should just the one van stall be sufficient for satisfying 11B-202.4?
  9. ADAguy
    Sep 11, 2013
    4,532
    431
  10. Yikes
    Yikes Gold Member
    Nov 2, 2009
    1,591
    201
    (I reference that it is a religious organization to note their exemption from ADA lawsuits; this is purely a CBC -11B compliance issue for the remodel, on a parking lot already approved by the AHJ several years ago.)
  11. north star
    north star Sawhorse
    Oct 19, 2009
    3,863
    283
    IMO, ...Yes, you have satisfied the Accessibility POT.......In your jurisdiction, is there a
    precedent for having an Accessible POT for "all" Accessible Parking Spaces, or is it a
    "Gray Area" to be determined by the AHJ ?
  12. JPohling
    JPohling Sawhorse
    Aug 16, 2011
    1,149
    149
    Agreed!
  13. mark handler
    Oct 25, 2009
    10,658
    901
    IMHO, No. But that is up to the AHJ and the CASp.
    Yikes likes this.
  14. ADAguy
    Sep 11, 2013
    4,532
    431
    Careful MH, CASps can only opinion unless they are an AHJ. Theirs is a "voluntary" certification, overseen by the state.
  15. mark handler
    Oct 25, 2009
    10,658
    901
    Certification, Which is recognize by the courts.
    Yikes likes this.
  16. ADAguy
    Sep 11, 2013
    4,532
    431
    Accepted by state but up to feds to accept or reject.
  17. Yikes
    Yikes Gold Member
    Nov 2, 2009
    1,591
    201
    I agree, Mark. But when it comes to being a sounding boards on accessibility questions on this forum, you are analogous to "Mikey" in the old Life Cereal commercials: if I can get you to 'like' something, chances are good that most everyone else (incl. AHJ and CASp) will eventually 'like' it too.
    (And I seriously mean this as a major compliment to you!)
  18. nealderidder
    Dec 7, 2010
    196
    9
    Nope, not a change of use.
  19. nealderidder
    Dec 7, 2010
    196
    9
    Thanks for all the feedback, looks like my thread got quasi-hijacked but I appreciate the responses!
  20. Ty J.
    Ty J. Sawhorse
    Aug 2, 2017
    1,135
    415
    Be very careful in your use of change of occupancy. Per the Ch. 2 definition, it is:
    [A] CHANGE OF OCCUPANCY. A change in the use of a building or a portion a building which results in one of the following:
    1. A change of occupancy classification.
    2. A change from one group to another group within an occupancy classification.
    3. Any change in use within a group for which there is a change in application of the requirements of this code.
    #3 can trip you up. Some occupancy types have requirements that are specific to a use, not just the occupancy classification.