• Welcome to The Building Code Forum

    Your premier resource for building code knowledge.

    This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.

    Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.

    Ready to upgrade? Log in and upgrade now.

Download UL White Book

Mr_Burns.png


Excellent, thanks.
 
UL always gave away there disks at our state meetings but it has always been more useful to download it. It is amazing what you find in there that gets overlooked in the field.

For instance a hub on a meter is not listed for a pvc thread only rigid metal and IMC. Now how many violations of that have you seen.
 
Dennis said:
For instance a hub on a meter is not listed for a pvc thread only rigid metal and IMC. Now how many violations of that have you seen.
Thats funny, took Jeff to work with me today. I used a PVC TA in a meyers hub and asked him if it was a violation. Got him with that one. (But I used it anyway)
 
ICE said:
It looks as though the box above is the support for the box below.
Ha ha, it does look like that but the trough below helped the most. This picture was before it was anchored and the equipment ground was added. I know there will be a grounding comment so l figured I might as well throw that out there now.
 
jar546 said:
I did not even know it was not listed for that application .
Here is the link to Mark Ode's paper I told you about.

Many electricians overlook the fact that hubs are only intended for use with threaded conduit, such as rigid metal conduit (RMC) or intermediate metal conduit (IMC). The hubs are designed with a tapered thread to match the tapered thread requirement of RMC or IMC of a 1-in-16 taper ( inch per foot taper) as covered in 342.28 for IMC and in 344.28 for rigid metal conduit.
 
Many electricians overlook the fact that hubs are only intended for use with threaded conduit, such as rigid metal conduit (RMC) or intermediate metal conduit (IMC). The hubs are designed with a tapered thread to match the tapered thread requirement of RMC or IMC of a 1-in-16 taper ( inch per foot taper) as covered in 342.28 for IMC and in 344.28 for rigid metal conduit.
So if you used a plumbing fitting it would actually be better ;)
 
Not Jeff's jurisdiction. Also had a couple PVC fittings I 'forgot' to glue. Violation IMO, can't you cite the art. that would pertain?
 
chris kennedy said:
Not Jeff's jurisdiction. Also had a couple PVC fittings I 'forgot' to glue. Violation IMO, can't you cite the art. that would pertain?
There is no article that specifically states you must glue the joints (unlike the plumbing code) but, there is the word approved that comess into play and we all know that is at the discretion of the AHJ. See 352.48

This ATS is, in my opinion and Industrial Control Panel and is subject to 409.100 which used table 110.20 so it does need to be protected. If the conduit leaks, then we have a problem, especially since it is above the live parts.
 
gfretwell said:
You are left with 110.3(B) for the cement requirement and, unfortunately, the manufacturers say you must use their glue.
I couldn't live with myself knowing the PVC was stressing when trying to expand due to the glue. Still trying to find 1 manufacturer that states glue must be used on all joints anyway.
 
jar546 said:
Still trying to find 1 manufacturer that states glue must be used on all joints anyway.
See this, its from the link you provided in post 1 of this thread. See 1.1.4

1.1.4 Rigid PVC conduit and fittings covered in these requirements are intended to be joined to each other and to rigid PVC boxes, conduit bodies, and fittings in the field by means of a cement that is or contains a solvent for polyvinyl chloride.
 
Back
Top