Thats funny, took Jeff to work with me today. I used a PVC TA in a meyers hub and asked him if it was a violation. Got him with that one. (But I used it anyway)Dennis said:For instance a hub on a meter is not listed for a pvc thread only rigid metal and IMC. Now how many violations of that have you seen.
You are probably going to hell because of that.chris kennedy said:(But I used it anyway)
Ha ha, it does look like that but the trough below helped the most. This picture was before it was anchored and the equipment ground was added. I know there will be a grounding comment so l figured I might as well throw that out there now.ICE said:It looks as though the box above is the support for the box below.
Here is the link to Mark Ode's paper I told you about.jar546 said:I did not even know it was not listed for that application .
Many electricians overlook the fact that hubs are only intended for use with threaded conduit, such as rigid metal conduit (RMC) or intermediate metal conduit (IMC). The hubs are designed with a tapered thread to match the tapered thread requirement of RMC or IMC of a 1-in-16 taper ( inch per foot taper) as covered in 342.28 for IMC and in 344.28 for rigid metal conduit.
So if you used a plumbing fitting it would actually be betterMany electricians overlook the fact that hubs are only intended for use with threaded conduit, such as rigid metal conduit (RMC) or intermediate metal conduit (IMC). The hubs are designed with a tapered thread to match the tapered thread requirement of RMC or IMC of a 1-in-16 taper ( inch per foot taper) as covered in 342.28 for IMC and in 344.28 for rigid metal conduit.
There is no article that specifically states you must glue the joints (unlike the plumbing code) but, there is the word approved that comess into play and we all know that is at the discretion of the AHJ. See 352.48chris kennedy said:Not Jeff's jurisdiction. Also had a couple PVC fittings I 'forgot' to glue. Violation IMO, can't you cite the art. that would pertain?
I couldn't live with myself knowing the PVC was stressing when trying to expand due to the glue. Still trying to find 1 manufacturer that states glue must be used on all joints anyway.gfretwell said:You are left with 110.3(B) for the cement requirement and, unfortunately, the manufacturers say you must use their glue.
See this, its from the link you provided in post 1 of this thread. See 1.1.4jar546 said:Still trying to find 1 manufacturer that states glue must be used on all joints anyway.
1.1.4 Rigid PVC conduit and fittings covered in these requirements are intended to be joined to each other and to rigid PVC boxes, conduit bodies, and fittings in the field by means of a cement that is or contains a solvent for polyvinyl chloride.