1. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

Egress Swing Direction

Discussion in 'Commercial Building Codes' started by Mostafa Magdy, Oct 30, 2019.

  1. Mostafa Magdy

    Mostafa Magdy Registered User

    Joined:
    Oct 30, 2019
    Messages:
    6
    Likes Received:
    0
    Hello, that's my first thread here and I'm sure it will not be the last one we have a new project that we are working on, it's an academic building located in Alamin Egypt, we have almost all rooms occupant load exceeds 50 which require more than egress door in the room, in addition, making the door swing direction outside the room but making swing direction outside makes the overall plan looks weird any suggestion, ideas or exception for swing direction.

    PS. I don't know how to upload an image here kindly advise.
     
  2. jar546

    jar546 *****istrator

    Joined:
    Oct 16, 2009
    Messages:
    7,227
    Likes Received:
    554
    Welcome. You can put the photo on a free service and post the link.
     
  3. Mostafa Magdy

    Mostafa Magdy Registered User

    Joined:
    Oct 30, 2019
    Messages:
    6
    Likes Received:
    0
    I've uploaded it here https://ibb.co/SymnRs0
    Thank you jar

    Capture.png
     
    #3 Mostafa Magdy, Oct 30, 2019
    Last edited by a moderator: Oct 30, 2019
  4. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    16,794
    Likes Received:
    1,082
    II
    Why does it make it look weird?

    What building code and year are you using?

    What grade level is this school?

    Cannot always have pretty
     
    #4 cda, Oct 30, 2019
    Last edited: Oct 30, 2019
  5. e hilton

    e hilton Bronze Member

    Joined:
    Jul 2, 2014
    Messages:
    586
    Likes Received:
    131
    If i am ready that right, all the doors swing in.
     
  6. Mostafa Magdy

    Mostafa Magdy Registered User

    Joined:
    Oct 30, 2019
    Messages:
    6
    Likes Received:
    0
    It looks weird if the swing direction was outside because we have plenty of doors due to occupant load.
    The building is an Academic For Hospitality Management.
    I'm using IBC 2015
     
  7. Mostafa Magdy

    Mostafa Magdy Registered User

    Joined:
    Oct 30, 2019
    Messages:
    6
    Likes Received:
    0
    They are, But they should swing the opposite direction.
     
  8. Rick18071

    Rick18071 Sawhorse

    Joined:
    Nov 28, 2009
    Messages:
    2,225
    Likes Received:
    276
    1010.1.2.1 Direction of swing. Pivot or side-hinged
    swinging doors shall swing in the direction of egress
    travel where serving a room or area containing an occupant
    load of 50 or more persons or a Group H occupancy.

    No exceptions!
     
  9. Pcinspector1

    Pcinspector1 Platinum Member

    Joined:
    Oct 28, 2009
    Messages:
    3,044
    Likes Received:
    408
    I've seen a lot of school classrooms with the door set back into the room with the door swing into the corridor or hallway. The door is allowed to swing into the corridor depending on the width of the corridor.

    IBC2012 section 1008.1.1.1 projections into the clear width shall not exceed more than 4-inches. Most likely due to a blind persons cane detection.
     
    my250r11 and Mostafa Magdy like this.
  10. Pcinspector1

    Pcinspector1 Platinum Member

    Joined:
    Oct 28, 2009
    Messages:
    3,044
    Likes Received:
    408
    Added: I've seen were the wall is inset and the door swings back into the wall when opened, taking space from the classroom, this keeps the door from projecting into the corridor.

    Hardware on a door like a closer would be permitted into the corridor not to exceed 4-inches.
     
    Mostafa Magdy likes this.
  11. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    16,794
    Likes Received:
    1,082


    What is the Square footage of the room??

    What factor are you using for occupant load?

    So adult education?
     
  12. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    16,794
    Likes Received:
    1,082

    I see two doors only out of room 56
     
  13. Mostafa Magdy

    Mostafa Magdy Registered User

    Joined:
    Oct 30, 2019
    Messages:
    6
    Likes Received:
    0
    I've seen this also and I'm considering it.
     
  14. Mostafa Magdy

    Mostafa Magdy Registered User

    Joined:
    Oct 30, 2019
    Messages:
    6
    Likes Received:
    0
    I use multiple codes to calculate occupant load as it must comply with the Egyptian code, as I said, occupant load exceeds 50 in almost all spaces which require 2 doors swinging out
     
  15. JPohling

    JPohling Sawhorse

    Joined:
    Aug 16, 2011
    Messages:
    1,029
    Likes Received:
    117
    Ok, so I am unsure of your question? You know the code requires the doors to swing in the direction of egress so swing them in the proper direction.
     
  16. Pcinspector1

    Pcinspector1 Platinum Member

    Joined:
    Oct 28, 2009
    Messages:
    3,044
    Likes Received:
    408
    Check classroom occupant load, 49 comes to mind for one exit access for an E-occupancy. Check your egress travel, may need additional class room exiting door? See section 1015.
     
  17. JPohling

    JPohling Sawhorse

    Joined:
    Aug 16, 2011
    Messages:
    1,029
    Likes Received:
    117
    he actually states that.............it must comply with the Egyptian code, as I said, occupant load exceeds 50 in almost all spaces which require 2 doors swinging out.............So I really am not sure why the question?
     
    Pcinspector1 likes this.
  18. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    16,794
    Likes Received:
    1,082
    Sounds like cosmetic
     
  19. my250r11

    my250r11 Sawhorse

    Joined:
    Feb 16, 2015
    Messages:
    575
    Likes Received:
    160
    Pcinspector1 has it. Recess, create an alcove, what ever you want to call it. General about 3.5ft to allow for a clear corridor.
     
    ADAguy likes this.
  20. e hilton

    e hilton Bronze Member

    Joined:
    Jul 2, 2014
    Messages:
    586
    Likes Received:
    131
    Thank you ... my thoughts exactly.
     
    JPohling likes this.