Now you are getting to where the rubber meets the road, wouldn't the distance to exits exceed 150'?
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
Now you are getting to where the rubber meets the road, wouldn't the distance to exits exceed 150'?
I would not approve it without more info
And documentation of use
You can what if it all day long and get different answers to the what ifs. Simple answer is yes exiting from the B through the S occupancy is still permitted. Find a code section that limit the number of people that can exit from a B through an S. Find a code section that requires a corridor be installed remember they are still part of the exit access. Find a code section that prohibits a less than 750 sq ft conference room within that what if 4,000 sq ft upper level office that may have a meeting of employees and outside clients in it that prohibits it construction or use. We might not agree or like it but the code allows it allOk
What if
100000 sq ft warehouse
Business wants to put a 4000 sq ft office space in the middle of the warehouse.
No rated corridors
If this one office is allowed,, because person knows way out
Will the 4000 sq ft office be allowed??
10% or less of the story in which it/they are located is the current IBC limit for 'accessory' uses, that is an accumulative 10% by the way.5,500 sf office occ>50 in a 55,00sf warehouse.
The 2nd exit for office can pass through the S1/S2 warehouse?
Is the 10% office area accessory to warehouse documented as currently 2015IBC applicable or is that just inferred from the SBCCI logic?
I disagree all B’s cannot exit thru an S
But what if a?