I work for a county in Wa. St. Our electrical permitting, plan review and inspections are handled entirely separate, by the State. The extent of our involvement is verifying that electrical has been approved at certain phases, prior to continuing. That being said, I am not the most electrically literate, so forgive my layman wording of things, but am trying to bring resolution to an inspection write up. Any and all help and comments are appreciated.
Situation: New construction of a large (8000 sqft) SFR. There is a garage with living space above it about 6 feet away. There is a connecting breezeway, which is only about 4 feet wide and actually is part of the support of a deck above.
We permitted this as one structure because they were attached.
The electrician filed for his permit and the plan checker/inspector at that time approved his design. The state rotates inspectors every year so they have a new inspector writing them up for the following violation. I will try to describe it as best as possible.
The property has an 800A service (green box). At that service, the electrician installed 4 200A disconnects. These feed 2 panels in the house and one in the garage building and the 4th is unused.
Each sub-panel has its own disconnect as well. The electrical inspector told them since this is considered a single structure, the disconnects have to be grouped. His reason for this was NEC 230.72A.
After some discussion, the inspector told the electrician he would accept a note from the building department stating that this is in fact, 2 separate structures, then the configuration would be allowed. If not, he would need to move the disconnect for the garage panel to the main house.
I could require them to provide a full 2 hour fire wall to establish 2 separate structures, however, I don't want to make the contractor do anything unnecessary.
My questions for the electrical folks on this forum are this:
Does my explanation make sense? I will provide more details if needed.
Would the disconnects at the 800A service box satisfy the requirement of "grouping" per the section cited?
Is this a legitimate write up by the electrical inspector?
I guess I am not clear what good me writing a letter stating this is 2 separate structures does, other than satisfy the electrical inspector. I don't want to approve something that is inherently unsafe.
Thanks again, in advance, for all feedback.
Situation: New construction of a large (8000 sqft) SFR. There is a garage with living space above it about 6 feet away. There is a connecting breezeway, which is only about 4 feet wide and actually is part of the support of a deck above.
We permitted this as one structure because they were attached.
The electrician filed for his permit and the plan checker/inspector at that time approved his design. The state rotates inspectors every year so they have a new inspector writing them up for the following violation. I will try to describe it as best as possible.
The property has an 800A service (green box). At that service, the electrician installed 4 200A disconnects. These feed 2 panels in the house and one in the garage building and the 4th is unused.
Each sub-panel has its own disconnect as well. The electrical inspector told them since this is considered a single structure, the disconnects have to be grouped. His reason for this was NEC 230.72A.
After some discussion, the inspector told the electrician he would accept a note from the building department stating that this is in fact, 2 separate structures, then the configuration would be allowed. If not, he would need to move the disconnect for the garage panel to the main house.
I could require them to provide a full 2 hour fire wall to establish 2 separate structures, however, I don't want to make the contractor do anything unnecessary.
My questions for the electrical folks on this forum are this:
Does my explanation make sense? I will provide more details if needed.
Would the disconnects at the 800A service box satisfy the requirement of "grouping" per the section cited?
Is this a legitimate write up by the electrical inspector?
I guess I am not clear what good me writing a letter stating this is 2 separate structures does, other than satisfy the electrical inspector. I don't want to approve something that is inherently unsafe.
Thanks again, in advance, for all feedback.