Emergency lighting
Manufacturers specs will have correct mounting height and Manufacturer can provide info about light levels at various ranges. If not supplied with the application, just ask for it.
I only looked at one spec
And I did not see anything like mount it this high and you will get this sq ft of candle power??
Not sure if it exists?
Any other chime ins?
Do you check to see if emergency lighting on final??
cda,
What you may be referring to is the Photometrics of
your particular lighting fixture.
This link to only one manufacturer, but down towards
the bottom, it shows the photometrics of their fixture.
It also provides the mounting heights and coverage
areas.
http://www.acuitybrandslighting.com/library//ll/documents/specsheets/elm2%20led.pdf
We do not [ typically ] actually measure the lumens at
1 ft. above the floor level, but we probably should.
We also do not have a lumens measuring meter.
  • Like
Reactions: cda
cda,
areas.
You are correct
I only looked at one maker, and did not see it on thier link.
I did not know it it existed or the manufacture put on the installer or ahj to figure it out
Thanks
If you have a particular manufacturer or brand that you
want information on, please provide that info, and I will
try to assist you.
Thanks !
try to assist you.
Thanks !
Just had a slow day, one day
Saw an emergency light on the wall
1.And wondered, self, is there a specific mounting height specified by the manufacture, to achieve one candle foot
2. Does anyone ask for those specs
3. Does anyone check in the field to see if they were installed correctly
We check plans and site to make sure they are there, but the Fire Marshall does the inspection of the fire alarms and and emergency lighting here, not sure he does anything other than make sure they work, but only guessing
Simple calculation. F.C.= Lumens / Distance in Feet squared.(Feet x Feet)
Lamp lumen output will decline over time. This varies by lamp type.