This is where we get a little too involved and give fuel to Mark K. The code clearly states the alarm comply with UL2017. The product being used is a pool alarm that is listed and labeled and clearly states UL2017. Why do we need to involve ourselves any more than this? It is not our job to do background investigations on equipment that is provided by the contractor or owner.
R4501.17.1.9
Where a wall of a dwelling serves as part of the barrier, one of the following shall apply:
- 1.All doors and windows providing direct access from the home to the pool shall be equipped with an exit alarm complying with UL 2017 that has a minimum sound pressure rating of 85 dBA at 10 feet (3048 mm). Any deactivation switch shall be located at least 54 inches (1372 mm) above the threshold of the access. Separate alarms are not required for each door or window if sensors wired to a central alarm sound when contact is broken at any opening.
Exceptions:
- a.Screened or protected windows having a bottom sill height of 48 inches (1219 mm) or more measured from the interior finished floor at the pool access level.
- b.Windows facing the pool on floor above the first story.
- c.Screened or protected pass-through kitchen windows 42 inches (1067 mm) or higher with a counter beneath.