Exam room flags - protuding objects

fw.

Bronze Member
Joined
Oct 21, 2009
Messages
56
Location
Minnesota
I am reviewing the plans for an outpatient clinic; the plans show those flip flags next to the exam room doors mounted at 72 inches to the center of the object. When folded against the wall they do not protrude more than 4"; they do extend more than 4" when flipped out into the hall. I see them like this everywhere else. Thoughts that since they fold back that they are in compliance with ANSI A117.1 section 307?

Thanks.
 
Any obstacle greater than 4" including "flip flags", are an obstacle.

Welcome to the forum

ICCA2008102312370131556.jpg
 
Last edited by a moderator:
There must be alternatives - can the flags be raised another eight inches to be above 80" ?
 
Mac said:
There must be alternatives - can the flags be raised another eight inches to be above 80" ?
Yes you can

There are also compliant "exam room signal flags" 4" or less

36851.jpg
 
Thanks, I thought they would be a violation. I think some of the nurses might be to short to reach if they are above 80".
 