exempting ANSI 117.7
Mr. Inspector
Poconos/eastern PA
It's intresting that different states have different codes for accessablity. Here in PA we use the IBC which refers to ANSI 117.7. Do other states that use something different for accessiblity but use the IBC exempt ch. 11, and sec. 1007 (means of accessible egress), and appendix E (supplementry accessible requirments) :?: Or do they just replace ANSI 117.1 with somthing else :?:
It's to bad that we are not on the same boat with this. :roll:
Re: exempting ANSI 117.7
Rick - Here in NYS we use the provisions in the Code as modified by Ansi A-117.1 (not 117.7 ;) ). The more restrictive provisions apply in the case of a conflict.
Most likely if you are not going to reference ANSI A117.1 in your code, you will be replacing much of Chapter 11.
For exampe without A117.1 it doesn't make any sense to refer to TYPE A and B dwelling units.
I was going to post this in the thread "Ramp that's not a ramp", but, this looks just as good. ADA questions of the month come out as often as revisions to the ADA. The following is the only question of the month that exists at ada.gov.
(Don't peek at the answer.)
ADA Certification Question of the Month July 2003
Which authority listed below can architects, builders and building owners in your jurisdiction rely upon in order to design and construct buildings and facilities that are accessible to and usable by persons with disabilities as required by title III of the Americans with Disabilities Act (ADA)?
(a) The title III ADA accessibility requirements for new construction and alterations of buildings and facilities, which include the ADA Standards for Accessible Design at 28 C FR Part 36, Appendix A.
(b) A state/local building code with accessibility requirements that have been certified by the Department of Justice as meeting or exceeding the title III ADA requirements for the accessibility of buildings and facilities.
© A state/local building code with accessibility requirements that have not been certified by the Department of Justice as meeting or exceeding the title III ADA requirements for accessibility of buildings and facilities.
(d) either a or b.
Answer: d.
"In jurisdictions that have received certification from the Department of Justice, design and construction professionals, and building owners can generally refer to the accessibility requirements of the certified code to determine what is required in order to comply with the accessible design standards of the ADA.
In those jurisdictions that do not have a code that has been certified as ADA equivalent by the Department of Justice, reference must be made to the federal ADA accessibility requirements, which include the ADA Standards for Accessible Design, to determine what is required to comply with the ADA.
Design and construction professionals, and building owners who rely solely on the accessibility provisions of an uncertified state/local building code, i.e., one that has not been certified by the Department of Justice to be equivalent with the ADA accessibility standards, risk noncompliance with the ADA.
The bottom line: Designing and constructing buildings and facilities in compliance with ADA certified state/local codes will result in greater compliance with the ADA and significantly fewer ADA lawsuits. And, should someone file an ADA lawsuit, compliance with a certified code is rebuttable evidence of compliance with the ADA."
Link to ADA QOM: http://www.ada.gov/certqom.htm
Clear as MUD.
Is the ANSI 117.1 a "certified code", considered as equivalent to the ADA by the DOJ?
Not "officaily" but the DOJ is heading that way. That is one reason the updated 2004 ADA and ABA guidelines have not been formally adopted. The new ANSI A 117.7 is supposed to be the final solution, but it is having difficulting getting into final approval. This has been ongoing for several years.
In our latest adoption, we adopted the Illinois Accessibility Code (state code) plus we left in IBC Chapter 11 which references ANSI. We had deleted Chapter 11 previously. Since the IAC hasn't been updated since 1997 we felt better with both available. We also added a statement that the most restrictive applies.
From the Deptartment of Justice ADA website:
The Department has certified as equivalent to the ADA Standards for Accessible Design the Washington State Regulations for Barrier-Free Facilities, the Texas Accessibility Standards, the Maine Human Rights Act, as implemented by the Maine Accessibility Regulations, the Florida Accessibility Code for Building Construction, the Maryland Accessibility Code and the North Carolina Accessibility Code. Currently Texas, Maine, Florida, Maryland and North Carolina have in place ADA-certified accessibility requirements.
However, this list was dated 2006, so if any of these jurisdictions have updated thier accessibility code, it may no longer "conform"
The bottom line is that the new ANSI will be the standard if ICC and the Access Board can ever get it finished.
Thanks for the link CD.
It's we all do it this way because we have uniform codes unless admended. :roll: The answer varies by where one is enforcing the rules, where the plan was drawn and who's building the project.
Like I said in a previous post only had one group refuse doing it. Most want the place very accessible for all it's members.
Coug Dad,
At least for Washington State, that is no longer valid. When Washington State moved to the I-codes, we are now using ANSI. Washington State Regulations for Barrier-Free Facilities was publish in 1989 and it was very nice having it approved by the DOJ while it lasted, but now we're in the same boat as everyone else (waiting for official approval of ANSI). I believe Washington was the first jurisdiction to get approval by DOJ. We had very good set of barrier free regulations, so transition to ANSI was not much of an issue.
Highly unlikely to be certified, in my opinion.
First because A117.1 does not contain scoping provisions.
Second because A117.1 has sections relating to dwellings which don't fall under ADA Title III.
Third because portions of A117.1 are not compliant with ADA Title III as implimented through ADAAG.
Finally, because "The Ick" could never avoid fiddling with it every three years.
The ICC has been working with the DoJ to get the two documents coordinated. According to rules established at the federal level, the DoJ can only certify state "adopted" laws as being in compliance with the ADA guidelines. Hence, it cannot "certify" the ICC's IBC/A117.1 accessibility rules.
However, the DoJ has agreed to evaluate the IBC/A117.1 in comparison to current and proposed ADA guidelines. An article that explains this was in the ICC magazine:
http://www.iccsafe.org/newsroom/bsjourn ... _66-80.pdf
(hopefully you can open the file without having to log in)
I think it was posted above but, here again is the explanation from the DoJ on certification:
http://www.ada.gov/certcode.htm
btw: there have been no additional state certifications since 2005 except for North Carolina which just dumped their old home-grown Accessibility code for teh Chapter 11/A117.1 combination (with a few local modifications based on historical preference - always more restrictive, never less). Thus far, the DoJ has reviewed and agreed that the 2003 and 2006 IBC with A117.1 meet the intent of the ADA but refuse safe harbor designation.
Interestingly, HUD does grant safe harbor designation to the IBC/A117.1 combination but with one or two caveats depending on which edition is adopted. If the 2006 IBC with the 2003 A117.1 is adopted, then HUD grants them Safe Harbor status with the caveat that the designer must use the HUD guidelines if considering technical impracticalities for site access and usage.
Back to the original question:
Most areas in the country use the IBC/A117.1 combination is one edition combination or another. Even states where state law has some accessibility control but allows local adoption (Maine, Arizona, etc), most local adoptions use the IBC Chapter 11/A117.1 combination. For example: One town in Arizona recently adopted the 2006 IBC but stripped the Chapter 11 provisions to substitute a reference to the statewide Accessibility Rules only to discover that they were lessening the requirements from neighboring jurisdictions since that amendment did away with Type A and Type B dwelling unit designations. they went back to a straight line adoption.
Most states have statewide accessibility laws that are based on the ADA but which do not address plan review or inspection so they never get into the building code arena. New Jersey has its own Barrier Free Sub-code which is home grown but refers to the 2003 A117.1. Florida dumps the Accessible means of egress and Chapter 11 with a ADAAG substitution (with some modifications). Ohio keeps 1007 but dumps Chapter 11 and slips in an unmodified ADAAG. Texas has it's own Texas Accessibility Standards (TAS) with references to A117.1 while California has it's own highly detailed and uniquely sequenced set of accessibility rules. Some states have no statewide rules at all except to cover state projects and leave the whole thing to local jurisdictions to adopt (or not) any accessibility rules (e.g. Missouri).
So, as noted in a prior comment, it's a real mess. Fifty little countries doing whatever they want without consistency. Now you know why the feds were once considering mandating a national building code (oh, that WAS the initial reason why the ICC was created you may recall).
Ohio dropped Chapter 11 in the 2000 ICC issue, but now, Ohio does use Chapter 11 with modifications to tighten up the language and bring it in line with existing Ohio law for building types eg. agricultural buildings (U) are not regulated by the building code. We do use the July, 1994 ADAAG as adopted by DOJ.
Sorry, Dan. You're right (of course)! :oops:
I forgot that the change happened recently. A while back, we were trying to use the pending reg's as basis for an appeal with the state (didn't go well, but you probably figured that if you know the state board). :shock:
<<< See just goes to show what a mess the states have made of the whole thing. . . . . >>>
Gene - One relatively minor error in an incredibly informative post... Not bad for a guy who's been on the bench for a few weeks! ;) In case anyone had any doubts...
Heeeeeeeeeeee's Baaaaaaaaaaaaaaaaaaaaack!
Gene Boecker said:
The ICC has been working with the DoJ to get the two documents coordinated. According to rules established at the federal level, the DoJ can only certify state "adopted" laws as being in compliance with the ADA guidelines. Hence, it cannot "certify" the ICC's IBC/A117.1 accessibility rules.However, the DoJ has agreed to evaluate the IBC/A117.1 in comparison to current and proposed ADA guidelines. An article that explains this was in the ICC magazine:
1. DOJ can certify local codes. They need not be at the state level.
2. A117.1 is a safe harbor under the Fair Housing Act because the FHA falls outside the scope of ADA.
3. Florida's accessiblity requirements are far more straight forward to enforce because there are fewer of them and they don't change every few years.
4. Florida's requirements are far far easier to design to because the match Federal law which architects and engineers are required to follow.
5. The initial reason for "the Ick" was to protect the petty empires of the various code bodies in the face of NFPA 5000. The AIA and construction industries got behind it because "the Ick" was far easier to manipulate than NFPA.
Plans Approver said:
Ohio dropped Chapter 11 in the 2000 ICC issue, but now, Ohio does use Chapter 11 with modifications to tighten up the language and bring it in line with existing Ohio law for building types eg. agricultural buildings (U) are not regulated by the building code. We do use the July, 1994 ADAAG as adopted by DOJ.[/quote:3tt9dx3p]
Do you find it hard to enforce?
3. Florida's accessibility requirements are far more straight forward to enforce because there are fewer of them and they don't change every few years.
1. Yep. The original question was about states so that was what I was responding to.
2. (I thought that's what I said)
3. Disagree. There are numerous areas where Florida is vague such as accessible means of egress.
4. Arguably true but both the Access Board and the DoJ agree that the current ADAAG guidelines are out of date.
5. Wrong! NFPA started their 5000 effort after they took issue with ICC's "consensus process" and decided to play in their own sandbox. Both industry and the AIA played in both sandboxes. The adopting agencies across the country decided which was the better one to adopt and use. Sorry, Brudgers. I know this part too, too well. :)
3. Seeing as Florida's requirements for accessible means of egress are exactly the same as those of ADA, if you have trouble understanding Florida's requirements for Accessible means of egress, I advise you to stay out of the Accessibility design and consulting business. Without a firm grasp of those requirements, it is hard to see how one could give competent comprehensive professional advice to any client anywhere regarding accessibility.
4. The Access board is not responsible for ADA. The DOJ is obligated to abide by Congress's legislative intent. It is difficult to see the weaker requirements in A117.1 can be constructed as consistent with that intent.
brudgers said:
3. Seeing as Florida's requirements for accessible means of egress are exactly the same as those of ADA, if you have trouble understanding Florida's requirements for Accessible means of egress, I advise you to stay out of the Accessibility design and consulting business. Without a firm grasp of those requirements, it is hard to see how one could give competent comprehensive professional advice to any client anywhere regarding accessibility.4. The Access board is not responsible for ADA. The DOJ is obligated to abide by Congress's legislative intent. It is difficult to see the weaker requirements in A117.1 can be constructed as consistent with that intent.
3. :lol: :P to you too! ;)
4. Not exactly. The Access Board (formerly the Architectural Barriers and Transportation Barriers Removal Commission) is the body given authority for rule-making relative to accessibility issues at the federal level. Hence they are responsible for the ADA guidelines. They have no enforcement powers which are given to the DoJ for Title III - our primary area of concern.
The weaker requirements in the A117.1????
I suggest you look over the proposed ADA/ABA. The text is almost exactly the same as the 2003 A117.1. A117.1 has incorporated the more current thinking of the DoJ and Access Board (e.g. reach range, door approach, accessible egress). Bring your head out into the sunshine a bit more.
Not at all. During plan review I go through ADAAG then 1007 and Ch. 11 as applicable citing whichever provides the greater accessibility. Because we adopted ADAAG (Appendix A only), religious facilities are not exempted, makes that part easier.
Of course under ADAAG, any raised area under 3000 sf would typically be exempted.