Companies are always on the hook for ADA compliance for their employees. Even if the building had not burned, it would have required "readily achievable barrier removal." This would not be a building department requirement, but would be part of an ongoing obligation under U.S. civil rights law (don't expose yourself to a lawsuit).
But if your question is: "will the building department require accessibility upgrades as part of the fire repair work?", then the answer lies in CBC 11B, andit mainly relates to:
(1) whether you are just trying to get it back to its pre-fire conditions, or whether you are altering (11B-202.2) or adding (11B-202.3) to the building.
(2) If you are not altering or adding, but are only doing fire repair, does it meet the definition of "structural repair"?
(3) If the answer to #2 is "yes" then see 11B-202.4, which requires the following components to be made accessible, with some exceptions:
When
alterations or
additions are made to
existing buildings or
facilities, an accessible
path of travel to the specific
area of
alteration or
addition shall be provided. The primary accessible
path of travel shall include:
- A primary entrance to the building or facility,
- Toilet and bathing facilities serving the area,
- Drinking fountains serving the area,
- Public telephones serving the area, and
- Signs.
(4) The code section cited above has an exception #8 based on the cost of the project:
11B-202.4 exc. #8: When the
adjusted construction cost, as defined, is less than or equal to the current
valuation threshold, as defined, the cost of compliance with Section 11B-202.4 shall be limited to
20 percent of the
adjusted construction cost of
alterations, structural
repairs or
additions. When the cost of full compliance with Section 11B-202.4 would exceed
20 percent, compliance shall be provided to the greatest extent possible without exceeding 20 percent.
- When the adjusted construction cost, as defined, exceeds the current valuation threshold, as defined, and the enforcing agency determines the cost of compliance with Section 11B-202.4 is an unreasonable hardship, as defined, full compliance with Section 11B-202.4 shall not be required. Compliance shall be provided by equivalent facilitation or to the greatest extent possible without creating an unreasonable hardship; but in no case shall the cost of compliance be less than 20 percent of the adjusted construction cost of alterations, structural repairs or additions. The details of the finding of unreasonable hardship shall be recorded and entered into the files of the enforcing agency and shall be subject to Chapter 1, Section 1.9.1.5, Special Conditions for Persons with Disabilities Requiring Appeals Action Ratification.
- For the purposes of this exception, the adjusted construction cost of alterations, structural repairs or additions shall not include the cost of alterations to path of travel elements required to comply with Section 11B-202.4.
- In choosing which accessible elements to provide, priority should be given to those elements that will provide the greatest access in the following order:
- An accessible entrance;
- An accessible route to the altered area;
- At least one accessible restroom for each sex or one accessible unisex (single-user or family) restroom;
- Accessible telephones;
- Accessible drinking fountains; and
- When possible, additional accessible elements such as parking, signs, storage and alarms.