Michael Corbett
REGISTERED
2018 IBC, section 1019,3 allows two story exit access stairways that are not enclosed within a fire barrier. Comments? In a two story B-Use building can two exit access stairs be the only means of egress?
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
1. No comments; that has been a part of the code for a long time.2018 IBC, section 1019,3 allows two story exit access stairways that are not enclosed within a fire barrier. Comments? In a two story B-Use building can two exit access stairs be the only means of egress?
In Connecticut, under our State Supplement, 2015 IBC we have dropped Exc. No 1 which reads: 1. Exit access stairways and ramps that serve or atmospherically communicate between only two stories. Such interconnected stories shall not be open to other stories. Any other areas it may have relocated?1. No comments; that has been a part of the code for a long time.
2. Yes, provided the travel distance from the most remote point on the second story, down the stair, and to an exterior exit door is within the distance permitted.
In Connecticut, under our State Supplement, 2015 IBC we have dropped Exc. No 1 which reads: 1. Exit access stairways and ramps that serve or atmospherically communicate between only two stories. Such interconnected stories shall not be open to other stories. Any other areas it may have relocated?
Yes, per Section 1019.3 unless you can make the stair can comply with Condition #4.Hello
I’m in NY and building a school class E, my question is if I have 3 story interior stairway, this stairways also has an exit to the street, but i don’t need it for a means of egress i have enough without that stairs, does this stairs need to be fire rated and enclosed?
Thanks
Thanks for replyingYes, per Section 1019.3 unless you can make the stair can comply with Condition #4.