1. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

Exterior Deck

Discussion in 'Door & Hardware forum *Sponsored by Allegion*' started by LGreene, Feb 7, 2020.

  1. LGreene

    LGreene Corporate Supporter

    Joined:
    Oct 20, 2009
    Messages:
    1,114
    Likes Received:
    89
    I was contacted about an antique barn that has been repurposed as an event space. The calculated occupant load of the barn is 140 people based on the unconcentrated assembly occupant load factor and I will verify that they have at least 2 egress doors with panic hardware.

    Here's the question for you. There is a 3,000-SF deck attached to the barn, which has its own exits to grade (it's 1 story up). The local fire department is saying that the deck does not increase the allowable occupant load of the total event space, because people on the deck might enter the barn during inclement weather, thereby increasing the number of people in the barn above 140.

    I have never heard of this. I would have expected the barn and the deck to have two separate occupant loads, since each has its own means of egress. I also thought that the calculated occupant load was used for determining the required amount of egress width, the number of plumbing fixtures, etc. I didn't think the purpose was to establish the maximum number of occupants that the barn could hold. And if the fire department is trying to come up with that number, why not use the concentrated use factor and then check to make sure the barn has the means to support that number of people?

    Can you help educate me?
     
  2. fatboy

    fatboy Administrator

    Joined:
    Oct 17, 2009
    Messages:
    5,893
    Likes Received:
    628
    This may help;


    1004.2.1 Intervening spaces or accessory areas. Where

    occupants egress from one or more rooms, areas or spaces

    through others, the design occupant load shall be the combined

    occupant load of interconnected accessory or intervening

    spaces. Design of egress path capacity shall be

    based on the cumulative portion of occupant loads of all

    rooms, areas or spaces to that point along the path of

    egress travel.
     
    LGreene, Pcinspector1 and ADAguy like this.
  3. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    17,270
    Likes Received:
    1,149
    As long as the deck has two code complying exits,,, it should stand alone.

    Now if say one exit is back into the building, that is where exiting needs to be looked at.
     
    LGreene likes this.
  4. steveray

    steveray Sawhorse

    Joined:
    Nov 25, 2009
    Messages:
    6,961
    Likes Received:
    1,012
    They "could" put 10,000 people in the barn...Doesn't change the approved OL...
     
    LGreene likes this.
  5. ADAguy

    ADAguy Registered User

    Joined:
    Sep 11, 2013
    Messages:
    4,236
    Likes Received:
    405
    If the barn exits are at grade vs the deck being above grade then you may have an argument for them being separate occupancies but then the deck may not be accessible and "that" is another issue.
     
    LGreene likes this.
  6. JPohling

    JPohling Sawhorse

    Joined:
    Aug 16, 2011
    Messages:
    1,103
    Likes Received:
    132
    As long as both spaces have compliant exiting you should be fine.
    I would be more concerned about increased live load requirements on the floors for this new assembly occupancy.
     
    LGreene likes this.
  7. Pcinspector1

    Pcinspector1 Platinum Member

    Joined:
    Oct 28, 2009
    Messages:
    3,176
    Likes Received:
    447
    Confused:confused:

    Does toilet counts and ADA access to the deck come into play?
     
    ADAguy likes this.
  8. LGreene

    LGreene Corporate Supporter

    Joined:
    Oct 20, 2009
    Messages:
    1,114
    Likes Received:
    89
    That's a great question! I'm guessing that the accessible entrance/exit is through the building and the bathrooms are inside. Would that mean that the allowable occupant load for the barn + deck is equal to the occupant load of the barn, with no additional occupants for the deck?
     
  9. Builder Bob

    Builder Bob Sawhorse

    Joined:
    Oct 17, 2009
    Messages:
    2,312
    Likes Received:
    359
    I think the total occupancy would be limited by the infrastructure provided - i.e. the total number of plumbing fixtures provided. MOE is only regulated by the area served -
     