New construction:
I am working on a large unlimited area building, fully sprinkled.
IBC 907 doesn't seem to trigger a fire alarm for an S-1 use.
But S-1 does have similar fire area etc that F-1 would have if it was not sprinkled.
If S-1 have similar fire area and sprinkler requirements why does it not have similar fire alarm requirements.
As far as i can tell IBC does not require fire alarm for S-1 use, but just wanted to make sure i am not missing anything.
Also its for a garbage facility, and they will have some tall piles so it looks like it will have some high pile storage. i went through that area and see those requirements, but again don't see a trigger for fire alarm.
Why would F-1 have fire alarm requirements but not S-1???