1. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

Fire extinguisher locations in S-2 Self-Storage

Discussion in 'Commercial Fire Codes' started by NerdelbaumFrinkJr, Mar 11, 2020.

  1. NerdelbaumFrinkJr

    NerdelbaumFrinkJr Registered User

    Joined:
    Jun 7, 2019
    Messages:
    5
    Likes Received:
    0
    Single-story, 40' x 140' S-2 occupancy. Basically 2 rows back-to-back of 10'x20' self-storage units with roll up doors, stud divide walls with ply'd sheathing. 1 ADA unit at one end. 5,600 sq ft total, unheated, non-sprinkled. Per NFPA 10 and IFC 906, I understand the maximum travel distance to a fire extinguisher is 75 feet. But where do you put the fire extinguishers? Because all the units are locked and accessible by the individual renters (and the property owner). Can the owner just install a extinguisher in the middle unit along each sidewall and provide a sticker on the door 'Fire Exitinguisher Inside'?
     
  2. Ty J.

    Ty J. Sawhorse

    Joined:
    Aug 2, 2017
    Messages:
    1,148
    Likes Received:
    420
    Typically installed on the wall within an inset cabinet. Make sure to provide appropriate signage.
     
    NerdelbaumFrinkJr likes this.
  3. Ty J.

    Ty J. Sawhorse

    Joined:
    Aug 2, 2017
    Messages:
    1,148
    Likes Received:
    420
    Like this...

    [​IMG]

    Note that the red box hanging from the left wall is a cabinet with an extinguisher.
     
  4. Ty J.

    Ty J. Sawhorse

    Joined:
    Aug 2, 2017
    Messages:
    1,148
    Likes Received:
    420
    Sorry for the third post, but are you also providing fire sprinklers? Storage units such as these will often be used for the storage of furniture and mattresses.

    As such, IBC 903.2.9 #5 will require sprinkers if the facility is larger than 2,500sf. One thing to note here is that it does not specify fire area, but the total area of the occupancy. Simply using fire barriers every 2,500sf is not enough to omit sprinklers.

    903.2.9 Group S-1
    An automatic sprinkler system shall be provided throughout all buildings containing a Group S-1 occupancy where one of the following conditions exists:

    1. A Group S-1 fire area exceeds 12,000 square feet (1115 m2).
    2. A Group S-1 fire area is located more than three stories above grade plane.
    3. The combined area of all Group S-1 fire areas on all floors, including any mezzanines, exceeds 24,000 square feet (2230 m2).
    4. A Group S-1 fire area used for the storage of commercial motor vehicles where the fire area exceeds 5,000 square feet (464 m2).
    5. A Group S-1 occupancy used for the storage of upholstered furniture or mattresses exceeds 2,500 square feet (232 m2).
     
    ADAguy likes this.
  5. NerdelbaumFrinkJr

    NerdelbaumFrinkJr Registered User

    Joined:
    Jun 7, 2019
    Messages:
    5
    Likes Received:
    0
    Thanks for the helpful posts. This was permitted as S-2 occupancy, so #903.2.9 does not apply. It is not sprinkled. The fire extinguisher cabinet location is logical, given that any renter can access it easily. It is a self storage in rural Wisconsin, so I see the extinguisher getting stolen by bored teenagers.
     
  6. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    17,983
    Likes Received:
    1,253

    Most places have cameras today, and hopefully the place is a little secure???

    I vote for number 3 thread reply
     
  7. TheCommish

    TheCommish Sawhorse

    Joined:
    Sep 27, 2011
    Messages:
    1,014
    Likes Received:
    189
    what is that dinky fire extinguisher going to put out, by the time someone gets it the building will be a goner
     
  8. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    17,983
    Likes Received:
    1,253
    The car that is burning, while being unloaded
     
  9. TheCommish

    TheCommish Sawhorse

    Joined:
    Sep 27, 2011
    Messages:
    1,014
    Likes Received:
    189
  10. my250r11

    my250r11 Sawhorse

    Joined:
    Feb 16, 2015
    Messages:
    676
    Likes Received:
    202
    This is an interesting interpretation for me, my BO & FM both agree the that the fire barrier creates "seperate bldgs" there for NS.
     
  11. Ty J.

    Ty J. Sawhorse

    Joined:
    Aug 2, 2017
    Messages:
    1,148
    Likes Received:
    420
    Fire barriers create separate fire areas....only fire walls create separate buildings.

    And per the IFC interpretation (link below), the fire area is not the driving factor.

    http://www3.iccsafe.org/cs/committeeArea/pdf_file/FI_12_20_14.pdf
     
    my250r11 likes this.
  12. my250r11

    my250r11 Sawhorse

    Joined:
    Feb 16, 2015
    Messages:
    676
    Likes Received:
    202
    My bad meant Firewalls, the link you gave I will bring up to them. Thanks!
     
  13. ADAguy

    ADAguy Registered User

    Joined:
    Sep 11, 2013
    Messages:
    4,552
    Likes Received:
    435
    You can also alarm the extinguisher. Is there an onsite manager?
     