ICC's 2015 re-write of EERO's really complicated things from the previous Editions. Pay special ATTENTION to Tables 1006.3.2(1) and 1006.3.2(2) as referenced. Generally speaking, a sprinklered building with two exits off the Story DOES NOT require EERO's. The occupants (fire fighters) in the R Occupancy are considered non-transient (i.e. they are familiar with their surroundings, un-like a Hotel occupancy). If the "calculated" occupant load of the residential area is less than 16, the occupancy can be classified as an R3, if greater than 16 then the Occupancy is R2. Note, the R3 Occupancy has no handicap requirements (bad idea) and the R2 Occupancy must be Type B Accessible Sleeping and bathing units (better but still not great). What I have typically done is to provide fully accessible (ANSI A117) bathing facilities in the "public" accessible restroom and make the sleeping quarters Type B Accessible. Other Occupancies that are typical in a Fire Station are S2, B and A3 (meeting rooms).
Ken
Consider if not separate rooms but a shared dorm area with 60" privacy screens then no EERO?
Have to look at the book.
Typically a fire station cannot meet the requirements of a live/work unit, particularly those in red below; therefore, they will go mixed use instead.Curiously shooting from the hip, how does IBC/VCC 419 come in to play with live/work units under an R2 classification in a fire station ? I understand the concept from the commentary persuasion, but with the R2 nomenclature, in concert with a mixed use 508, have to ask...
I always get in trouble when I say typically, but do understand the point....Typically a fire station cannot meet the requirements of a live/work unit, particularly those in red below; therefore, they will go mixed use instead.
419.1.1 Limitations
The following shall apply to all live/work areas:
- The live/work unit is permitted to be not greater than 3,000 square feet (279 m2) in area;
- The nonresidential area is permitted to be not more than 50 percent of the area of each live/work unit;
- The nonresidential area function shall be limited to the first or main floor only of the live/work unit; and
- Not more than five nonresidential workers or employees are allowed to occupy the nonresidential area at any one time.
I don't disagree with you on that point for sure. Our station was not designed with sleeping quarters in mind as we have only very recently evolved into a combination department with staff spending the night. The room we converted to the sleeping area was the only other room besides the training room. I just want to make sure we are up to code with everything. The code book is very thorough and a bit overwhelming in spots.I don’t know what 1988 Oregon code said about a door from a sleeping room to a garage but here and now that would not be allowed.