Dave
Not sure how up on codes you are, so
In codes we start with the thing we are looking at.
Than look at the code book to see if it applies to what is being looked at.
One thing that is used is the "Scope" of the code and Chapter in question.
Once again the Scope of Chapter 8:
SECTION 801 GENERAL
801.1 Scope. Provisions of this chapter shall govern the use of materials used as interior finishes, trim and decorative materials.
This chapter contains requirements for materials used as interior finish, trim or decorative materials. These materials must conform to the flame spread index limitations, the heat release and flashover limitations or flame propogation limitations established by this chapter. This chapter is similar to Chapter 8 of the International Fire Code® (IFC®) in intent but is focused only on new construction and only on interior finish, trim and a limited amount of decorative materials. The IFC addresses both new and existing buildings and also some key building contents.
And once again definitions:::
INTERIOR WALL AND CEILING FINISH. The exposed interior surfaces of buildings, including but not limited to: fixed or movable walls and partitions; toilet room privacy partitions; columns; ceilings; and interior wainscoting, paneling or other finish applied structurally or for decoration, acoustical correction, surface insulation, structural fire resistance or similar purposes, but not including trim.
A material that is applied to ceilings as well as walls, columns, partitions (including the privacy partitions in bathrooms that could pose a significant threat in larger bathrooms if unrated) and other vertical interior surfaces whether fixed or movable. The application of this material may be for structural, decorative, acoustical, structural fire resistance and other similar reasons. Trim, such as baseboard, door or window casing, is not considered interior wall and ceiling finish. Interior wall and ceiling finish is regulated by Section 803.
And if you read, it tends to be more "Applied to"
I still think that Chapter 8 does not apply to your situation
Even Section 806:::
There are no F or S, which it sound like what your occupancy is, in the "General Requirements"::
SECTION 806 DECORATIVE MATERIALS AND TRIM [F]
806.1 General requirements. In occupancies in Groups A, E, I and R-1 and dormitories in Group R-2, curtains, draperies, hangings and other decorative materials suspended from walls or ceilings shall meet the flame propagation performance criteria of NFPA 701 in accordance with Section 806.2 or be noncombustible. [F]
In Groups I-1 and I-2, combustible decorative materials shall meet the flame propagation criteria of NFPA 701 unless the decorative materials, including, but not limited to, photographs and paintings, are of such limited quantities that a hazard of fire development or spread is not present. In Group I-3, combustible decorative materials are prohibited.
Fixed or movable walls and partitions, paneling, wall pads and crash pads applied structurally or for decoration, acoustical correction, surface insulation or other purposes shall be considered interior finish if they cover 10 percent or more of the wall or of the ceiling area, and shall not be considered decorative materials or furnishings.
In Group B and M occupancies, fabric partitions suspended from the ceiling and not supported by the floor shall meet the flame propagation performance criteria in accordance with Section 806.2 and NFPA 701 or shall be noncombustible.
Not sure how up on codes you are, so
In codes we start with the thing we are looking at.
Than look at the code book to see if it applies to what is being looked at.
One thing that is used is the "Scope" of the code and Chapter in question.
Once again the Scope of Chapter 8:
SECTION 801 GENERAL
801.1 Scope. Provisions of this chapter shall govern the use of materials used as interior finishes, trim and decorative materials.
This chapter contains requirements for materials used as interior finish, trim or decorative materials. These materials must conform to the flame spread index limitations, the heat release and flashover limitations or flame propogation limitations established by this chapter. This chapter is similar to Chapter 8 of the International Fire Code® (IFC®) in intent but is focused only on new construction and only on interior finish, trim and a limited amount of decorative materials. The IFC addresses both new and existing buildings and also some key building contents.
And once again definitions:::
INTERIOR WALL AND CEILING FINISH. The exposed interior surfaces of buildings, including but not limited to: fixed or movable walls and partitions; toilet room privacy partitions; columns; ceilings; and interior wainscoting, paneling or other finish applied structurally or for decoration, acoustical correction, surface insulation, structural fire resistance or similar purposes, but not including trim.
A material that is applied to ceilings as well as walls, columns, partitions (including the privacy partitions in bathrooms that could pose a significant threat in larger bathrooms if unrated) and other vertical interior surfaces whether fixed or movable. The application of this material may be for structural, decorative, acoustical, structural fire resistance and other similar reasons. Trim, such as baseboard, door or window casing, is not considered interior wall and ceiling finish. Interior wall and ceiling finish is regulated by Section 803.
And if you read, it tends to be more "Applied to"
I still think that Chapter 8 does not apply to your situation
Even Section 806:::
There are no F or S, which it sound like what your occupancy is, in the "General Requirements"::
SECTION 806 DECORATIVE MATERIALS AND TRIM [F]
806.1 General requirements. In occupancies in Groups A, E, I and R-1 and dormitories in Group R-2, curtains, draperies, hangings and other decorative materials suspended from walls or ceilings shall meet the flame propagation performance criteria of NFPA 701 in accordance with Section 806.2 or be noncombustible. [F]
In Groups I-1 and I-2, combustible decorative materials shall meet the flame propagation criteria of NFPA 701 unless the decorative materials, including, but not limited to, photographs and paintings, are of such limited quantities that a hazard of fire development or spread is not present. In Group I-3, combustible decorative materials are prohibited.
Fixed or movable walls and partitions, paneling, wall pads and crash pads applied structurally or for decoration, acoustical correction, surface insulation or other purposes shall be considered interior finish if they cover 10 percent or more of the wall or of the ceiling area, and shall not be considered decorative materials or furnishings.
In Group B and M occupancies, fabric partitions suspended from the ceiling and not supported by the floor shall meet the flame propagation performance criteria in accordance with Section 806.2 and NFPA 701 or shall be noncombustible.