Is there code language that allows the use of flashing instead of PT? I only see PT or naturally durable as an option in R317...
Since it's not common (at least where I'm at) to use PT sheathing, we will often see flashing like you're describing.
Sorry, I approached it from the “new posts” link and missed that. My bad. My question remains about the IBC, though.The question is posted in the "Residential Building Codes" discussion area. I think we can assume it's a residential project.
Yes, there is similar in CBC. "2304.12 Protection against decay and termites."Sorry, I approached it from the “new posts” link and missed that. My bad. My question remains about the IBC, though.
On my nonresidential projects we have gravel in lieu of planters where it’s close to the low-threshold entry doors.
Not exactly, that was my point. It's not explicitly spelled out, but statements like "unless separated from such slab by an impervious moisture barrier" or "exposed to the weather" cover all of the various situations that could arise.Is there code language that allows the use of flashing instead of PT? I only see PT or naturally durable as an option in R317
R317.1 Location required. Protection of wood and wood based products from decay shall be provided in the following locations by the use of naturally durable wood or wood that is preservative-treated in accordance with AWPA U1.
Sorry for the confusion - it is residential, looking specifically for an IRC reference. The most important detail is the one you leave out haha!The OP didn’t state this was a residential project - - are there comparable requirements in the IBC as well?
In general practice, when renovating existing buildings where framing was too close to grade, I'll specified waterproofing protected by flashing and not had an issue getting it approved. However I've worried that if the building official objected, I had no grounds in the code to justify our design.Not exactly, that was my point. It's not explicitly spelled out, but statements like "unless separated from such slab by an impervious moisture barrier" or "exposed to the weather" cover all of the various situations that could arise.
I think the scenario you're describing falls under item five that I quoted above. By installing the flashing, you are removing the exposure to weather. If it's no longer "exposed to the weather", then it is not required to be protected by some other means such as PT.